Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss New build dwelling >200mt/2 fire alarm in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Hi all

    We have been invited to tender for a new build dwelling, two storey with a ground floor of 240mt/2. My understanding of Part B is the property will require a Grade B-LD3 fire alarm system. My tender allowed for a LD2 to include high risk areas, kitchen and living room (wood burner)

    The developer has since returned my tender questioning why I’ve included this system as none of the other tenders received has. I’ve sent Part B to him highlighting what is required of building regulations and I’m waiting on a reply.

    Are we the few who knows of these regulations? We do have to comply with all building regulations after all.

    Thoughts and comments.
     
  2. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Sounds very odd but I agree with the Grade of system you propose.
     
  3. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    In the end their Building Inspector will have to sign off and they will be looking for the right grade system. Hopefully :rolleyes:
     
  4. Vortigern
    Offline

    Vortigern Regular EF Member

    Location:
    England
    Business Name:
    F.H. Electrical
    My understanding is that it is the building owners responsibility to spec the fire alarm and emergency lighting system it is not up to me/you. Of course they will have to have regard to enforcing authorities and BSxxxx in terms of that spec. Had I put in a quote I would not have quoted for something not asked for either.
     
    • Agree Agree x 1
    • Disagree Disagree x 1
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you should have done alternative quotes, 1 price for LD2 and another (lower) price for LD3. then it would be up to the client (developer) to decide ( with BC agreement) on which level of system they want installing.
     
    • Agree Agree x 1
    • Disagree Disagree x 1
  6. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    unless it is on the plans .
     
  7. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Thanks all

    Further to my OP I have had opportunity to meet with the developer. It appears of all three tenders mine was the only one offering the Grade B-LD2 fire alarm system. The other two tenders, which I have not seen, apparently make no mention of any form of fire alarm other than smoke:heat:co detectors in certainly areas and I have assumed from this a Grade D system (Aico etc)

    The client also contacted his building control office while I waited and they also confirmed the need for a Grade B given the floor area. Do it appears our tender is correct.
     
    • Like Like x 1
  8. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Nothing more on the plans than the normal blurb BS5839-6:2013 to be honest and suggested location of detectors.
     
  9. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Thanks and I value your opinion but It is not my practice to provide multiple tenders for alternative none compliant options as these will be selected solely on price not suitability. It would be likely the completed project would fall short of building regulations as a LD3.
     
  10. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Thank you but the small print to the side of all drawings has to always be read as it is here the relevant standards are noted to which we should be adearing too.
     
  11. Markc
    Offline

    Markc CCTV / Alarms

    Location:
    Norfolk
    Hopefully yes. But also at that stage of sign off alterations to none compliant installation is very difficult to do.
     
  12. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    its not down to you where the detectors go it down to the architect he plans the building .e.g .socket switches .and smoke detectors .
     
    • Disagree Disagree x 1
  13. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Good to hear they've confirmed your design. Good luck with the tender ! :)
     
    • Like Like x 1
  14. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    Well I was about to question why a grade B was needed but a quick check of BS5839-6 shows that you are 90% correct:). i didn't know about the >200m2 bit!
    It does say 'might' be required though. I wonder what determines whether it is or isn't required for >200m2.
    The below quote is taken from BS5839-6:
    "Grade D is required for new, owner-occupied buildings of up to three storeys, two storey rented properties and existing, owner-occupied buildings of more than two storeys. Very large storeys (>200m2) might require Grade B alarm system."
     
  15. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I've always thought that was to cover where we might be told it needed it :)
     
Loading...
Similar Threads - build dwelling >200mt Forum Date
Running workshop power from another garden building Electrical Forum Tuesday at 9:41 PM
Blo*dy Builders!!!!!!!!!!!! Electrical Forum Apr 11, 2019

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job