Hi all,
Just quoting for some new build houses and need a bit of advice. The consumer units will be approx 8 metres from the cut out. What is the correct way of going about getting the tails to the board? I think its a case of a 25mm 2 core swa with a separate 16mm earth with a 100a double pole isolator next to the meter. Is this correct? Or do i need an 80a switched fuse instead of an isolator and or a 3 core swa instead of a 2 core?
Thanks.
Just quoting for some new build houses and need a bit of advice. The consumer units will be approx 8 metres from the cut out. What is the correct way of going about getting the tails to the board? I think its a case of a 25mm 2 core swa with a separate 16mm earth with a 100a double pole isolator next to the meter. Is this correct? Or do i need an 80a switched fuse instead of an isolator and or a 3 core swa instead of a 2 core?