Discuss new builds with no rcd protection?!? in the UK Electrical Forum area at ElectriciansForums.net

michaelw6

-
Arms
Reaction score
27
i have recently been into a couple of property's which are apartments with no rcd protection. there are about 40 of these apartments in this block all of which i assume are the same.
i have checked the main incomer which just goes through an isolator and 80a mcb to the apartment with two supplies, these go into a quickline 2 board with two main isolators either side split peak and off peak.
with 17th edition i did not think this would be aloud.

Im requesting they change the mcbs for rcbos what are your views in case ive missed something here!
 
When were the apartments designed?
If the design was made to the 16th edition, then there would have been no requirement for RCD protection, even if construction commenced after the 17th edition was introduced.
 
It's not an absolute requirement circuits are rcd protected.

Rcd's are often the most cost efficient way of satisfying bs7671 but not the only way.

Check the wiring systems.
 
Unless you use SELV for locations containing baths or showers, every 17th edition installation with such a location will require at least one circuit to have RCD protection.
 
you say apartments.

Skilled person present?

Janitor/care taker with relevant qualifications?


I agree they should have at least some rcd protection but just trying to think of why they wouldn't.

I guess you could also rule out use of exterior sockets/appliances on anything above ground floor.
 
Yup I agree I've been reading and I cant really see any valid loop holes as to why they wouldn't put them in.

either designed to 16th or not designed to bs7671 (not law don't forget) don't ask me how they got signed off though.
 
Yup I agree I've been reading and I cant really see any valid loop holes as to why they wouldn't put them in.

either designed to 16th or not designed to bs7671 (not law don't forget) don't ask me how they got signed off though.

yes 16th edition design i reckon.
but i dont thing there should be no rcd protection at all even 16 required some protection.
although both apartments i checked were not on ground floor...
 

Reply to new builds with no rcd protection?!? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
428
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
542
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock