hello all, can someone please advice me the best way of filling out EIC form when doing sub-main supplies.

I doing a log cabin installation and i have made the cabin a tt due to the supply being 30 meters away and being TN-CS.

The bit I'm not sure on is where, if at all, do i put the earth rod resistance of the cabin as I'm only recording the supply characteristics and i thought this maybe should noted some where.
I did a house rewire and new garage installation last month and noted on the certificate garage supply on it own line and wrote on under Zs colum the earth rod resistance and then started a new line with the garage circuits and after talking to a few others I'm now think i may of done it wrong and maybe should i have done 2 certificates but i dont really know so was hoping you guys could help me out with this one as i dont want to get it wrong especially twice.

thanks for any advice's
jim:)
 
You mention sub-main, I take you have a second board for the cabin then? If so then you would have a second schedule of test results, as each board must have its own schedule. So...

1 x page for client details etc.
1 x sheet for supply characteristics and earthing arrangements
1 x inspection schedule certificate
2 x shedule of test results

so on the second schedule of test results you would state it's a TT system and make a note of its earth electrode resistance.

Hope this helps!:D
 
Thanks for the quick reply, i think ive got it but just check i use elseca sheets which has on :-

sheet (1) - cilent details, supply characteristics and particulars of installation

sheet (2) - Shedule of items inspected and installed circuit details for 9 circuits

sheet (3) - Continuation sheet

so as i as understand i would want 1 x sheet (1) , 1 x sheet (2) with details of submain and a seperate continuation sheet ( sheet (3) ) for log cabin just showing circuit test results to which i make a note of earth rod resistance some where or do i use 1 x sheet (2) again

sorry to be a pain and thanks for replying brightspark
 

Reply to New Installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello folks, So my van got found after being stolen ;D Now I'm installing my own alarm on the van which is triggered when a door is opened. Im...
Replies
4
Views
488
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock