Discuss New member needing help with commercial max demand in the The Welcome Forum area at ElectriciansForums.net

Alot more info is needed to give you any help. Like what loads will be connected?
How long will they all be used for?
For starters, then could you post up your thoughts so we can see if you understand what your trying to undertake.
 
Yes sorry thought this was just an introduction.

It’s a Caribbean catering van,
The items running off power are as followed
3x rice warmers totalling 5600w
2x Bain Marie 4000w
1x heat cabnight 1800w
1x drink fridge 500w
1x meat fridge 350w
This will be running off a generator sometimes and sometimes commando supply so we are limited to what it can pull!
 
Welcome to the forum.

You have a heavy demand on that trailer for a standard electricity supply for a mobile unit, your maximum utilisation is about 60A.

Most mobile supplies tend to be 16A with a few 32A if you are lucky and you will need a fairly reasonable generator to provide that level of power.
I would suggest that the unit would need to be operated on a very conservative basis and due account taken of what is connected and switched on at any one time.
In practice the majority of operators assume infinite power at all times and take no consideration of possible overloads.
Because once in use the equipment will be going on and off on temperature, this does allow you some leeway but in general I would tend to try and arrange switching such that large demand items cannot be on simultaneously. Switching on would need to be staged to avoid a heavy overload initially.

Once all is in use then you should be able to operate on a 32A supply so long as due care is taken to limit heater use, e.g. rice warmers may not need to be on all the time once they are hot and could be switched off for a while if the lids are remaining in place at slow times or is it possible to use only one rice warmer depending on customer demand.
Running on a 16A supply would mean a limitation on what could be operated at once and so a cooking plan would need to be in place for these occasions.
Really you are trying to look at running only two or three of the high power kit at any one time.
 
Thank you for your reply, as aspected just wanted to confirm. Would you agree that putting the catering van on a 10k/ 12k generator would be best. Also having a 62a commando or 2x 32 a commandos for the supply input. Thanks
 

Reply to New member needing help with commercial max demand in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all new member here currently retraining to be an electrician 18 months in so far after being a plasterer since leaving school enjoying the...
Replies
7
Views
323
Hi new member, retired, apprentice trained and HNC qualified post City and Guilds trade qualification.
Replies
2
Views
263
Hi I’m installing a wallbox pulsar max in a few weeks and they don’t come with a CT is it even allowed to fit a EVCP without a CT clamp? Thanks
Replies
13
Views
1K
Hi, I need help with my catering van, I am looking to get leisure batteries for my catering van but don't know how many i need or what i need, i...
Replies
8
Views
702
Hi there : I am just posting to introduce myself, stop lurking (!) and to thank the many sparks who so freely share their expertise on this great...
Replies
3
Views
303

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock