Been asked to supply temporary 4 x 63a 3 phase supplies from a genny. All the info I have is that they are pulling about 61a on each so close to the top. I need to work out kw/kva of genny but can't remember the calculation for this. If single phase I would just 61×230(around 14kw).
For 3 phase I can't remember if I just times this by 3 or do 61x400. All feeds are running motors so are balanced and on the way I will be taking off some small single phase which shouldn't unbalance thing too much. Any help appreciated
Cheers
 
basically you use 61A x 3 x 400A = 73,200 VA or 73kVA.
 
GENERATOR AMP RATINGS - THREE PHASE EXTENDED
3 PHASE AMPERES - 80% POWER FACTOR*


kW Times 1000 divided by (Volts*1.73) *.80

This chart approximates the amperage of a generator based on the size of the generator and the load on the generator at 100 percent of capacity. Please note that this table is intended to be used as an estimator is not an exact representation due to various factors that can increase or decrease amperage. Elevation, temperature, fuel quality, age, wire size and length and other factors can decrease the amount of power a specific installation can generate.

Here is a link to a chart that gives you the information you require.
Generator Amp Ratings Chart, Three Phase Extended Custom - https://www.generatorjoe.net/html/genrate.html
 
Thanks for such a quick reply! Am I right in thinking then I'll need a 292kva genny total or 233kw using x 0.8?
no..... 73kVA total . (as you have stated the phase current, i've not considered PF).
 
Ok... Am I just being really thick.
The OP requires 4 feeds of 61A (3 phase)... Isn't that 244A?
According to a genny calc site that would be about 170kVA
upload_2018-1-15_11-24-48.png


If these are all running motors then the starting of the motors may affect the max amperage needed.
 
This is all simpler than I thought so I think I may be over complicating this in my head. Is it as simple as saying 61a x 230 = 14kw then x 3 for 3 phase (42kw) and then I want 4 so 168kw total (bit more for Kva) am I there or have I done this wrong
 
Been asked to supply temporary 4 x 63a 3 phase supplies from a genny

Please can you clarify this comment. What is it you actually need?
See post #6 & post #8
 
that's about right. i forgot that you'd got 4 supplies, so 42 x 4 = 168kVA. if the 61A current is a given, then forget about PF or kW-kVA. that's already allowed for if the 61A is correct.
 
Please can you clarify this comment. What is it you actually need?
See post #6 & post #8
Sorry yes the actual need is 4 separate 3 phase supplies at 63a so its 42kw for each 3 phase supply times 4. Thanks for your help guys. I had the answer originally and then completely over thought it. Back to basics
 
If the genny is powering 3 motors, that "are pulling about 61a" each, how are the motors controlled (DOL, inverter) and do they all start at the same time?
Would you not need a bigger genny for the start-up of the motors?
 
In truth,to accurately guage the size and type,there are many other factors to be considered,not least,installation earthing,duty cycles,fuelling and noise...

Just considering the possible running load,would only ensure reliability,for a day :)
 
If the genny is powering 3 motors, that "are pulling about 61a" each, how are the motors controlled (DOL, inverter) and do they all start at the same time?
Would you not need a bigger genny for the start-up of the motors?
Sorry spoon, I was given the wrong info, the power is for heating not motor and I can get them switched on and off individually via separate controls.
 
In truth,to accurately guage the size and type,there are many other factors to be considered,not least,installation earthing,duty cycles,fuelling and noise...

Just considering the possible running load,would only ensure reliability,for a day :)
I appreciate that there is more to it. This is for film production purposes so will only be there a week so not really a problem if we overkill it with a bigger genny then needed.
I have got a 200kva that supplies 250a each phase so I'm going to suggest using just three of the 3 phase 63a heaters as although the Kva rating is ok, we will be pushing about 183a down each phase from my calcs
 

Reply to New member, straight in with a question in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
535
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
606
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock