Discuss New sockets fault keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Hi I have put new socket in hall and ran cable straight to consumer unit,and connected to downstairs sockets . But it keeps tripping . I have used about 10 metres of cable .
Why would this be any help be grateful.
So you have spurred directly from the MCB ?is the CU a modern type ie does it have 2 RCDs?
Have you connected the N to the correct N bar?
 
I disconnected again but totally puzzled checked cable and changed sockets but still no joy .

View attachment 42516
Of the 2 N bars, which one are the existing RFC Ns connected too, whidhbar did you connect thre new N into, can you see what people are getting at? Have you IR tested your new addition?
 
Last edited:
Is it just me, or is there less neutral cables than there is live?

Problem could be at the socket. Live cable squashed against fixing lug for example.
 

Reply to New sockets fault keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
567
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
633
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock