Discuss Nic Eic Assessment When Dno Haven't Been To Replace Earthing in the UK Electrical Forum area at ElectriciansForums.net

N

Nuvo

Hi All what a day ive had.
ive just rewired a 2 bed house with TN-S arrangment. ive come to the testing and the ZE is reading 2.93 ohms. i installed new 16mm to the clamp that was originally on the incoming i cleaned up with the wire brush and tightened. still wouldnt bring it down. so ive called the DNO Western power theyve been out tonite and told me its not one of there earths they have not supplied an earth. they said they can strip back to lead core and provide me an earth for around 50-60 quid but wont be done till the middle of next week. Here is the big problem. i have my first NIC EIC assesment next tuesday so job wont be complete. would the nic eic refuse to see that job as i have no other to take them too. or could i possibly still take them there because i can show i can still test and show im going the right way about things and would be ok. the last thing i want to happen is for them to say its no good re arrange and charge me the 290 quid for rebooking. i was chatting to the western power fella he said to install a earth rod to a tt system but not keen on this idea what are your thoughts sorry if this is hard to understand but any advice will be greatly appreciated.
 
Hi All what a day ive had.
ive just rewired a 2 bed house with TN-S arrangment. ive come to the testing and the ZE is reading 2.93 ohms. i installed new 16mm to the clamp that was originally on the incoming i cleaned up with the wire brush and tightened. still wouldnt bring it down. so ive called the DNO Western power theyve been out tonite and told me its not one of there earths they have not supplied an earth. they said they can strip back to lead core and provide me an earth for around 50-60 quid but wont be done till the middle of next week. Here is the big problem. i have my first NIC EIC assesment next tuesday so job wont be complete. would the nic eic refuse to see that job as i have no other to take them too. or could i possibly still take them there because i can show i can still test and show im going the right way about things and would be ok. the last thing i want to happen is for them to say its no good re arrange and charge me the 290 quid for rebooking. i was chatting to the western power fella he said to install a earth rod to a tt system but not keen on this idea what are your thoughts sorry if this is hard to understand but any advice will be greatly appreciated.

You should have assessed the earthing arrangement before carrying out the work as per the regs. A clamp onto a sheath that has not been provided by the DNO is not suitable and your only option is to use a temporary rod until a DNO connection has been made. You are right, it's not ideal.
 
Erm... If I were you I would have wrapped up a job long ago to show them, not leave it until the last minute.

However, you are in this position now and need to come up with a plan.

If WPD won't come out any sooner, I would bang an earth rod in.
 
Seems kinda silly doing a TT with a probable Ra far exceeding the present 2.93 ohms!
I cant see a problem with connecting to that as a temporary measure and filling in your EIC but not completing it. Why not contact the NICEIC and ask them if that is acceptable pending the faulty TNS being rectified?
I assume the present high Ze will meet disconnection times via RCD's with your TNS designed install?
 
Hi All what a day ive had.
ive just rewired a 2 bed house with TN-S arrangment. ive come to the testing and the ZE is reading 2.93 ohms. i installed new 16mm to the clamp that was originally on the incoming i cleaned up with the wire brush and tightened. still wouldnt bring it down. so ive called the DNO Western power theyve been out tonite and told me its not one of there earths they have not supplied an earth. they said they can strip back to lead core and provide me an earth for around 50-60 quid but wont be done till the middle of next week. Here is the big problem. i have my first NIC EIC assesment next tuesday so job wont be complete. would the nic eic refuse to see that job as i have no other to take them too. or could i possibly still take them there because i can show i can still test and show im going the right way about things and would be ok. the last thing i want to happen is for them to say its no good re arrange and charge me the 290 quid for rebooking. i was chatting to the western power fella he said to install a earth rod to a tt system but not keen on this idea what are your thoughts sorry if this is hard to understand but any advice will be greatly appreciated.


Bang a rod in or prepare 349£ for a revist mate if not possible strip it back put a clamp yourself and play the game.
 
Not got the bottle to strip back myself. i will call them tomoz as its rcd protected table 41.5 inregs book allows the max zs not exceed 1667ohms. im in a bit of a rock and hard place
 
Not got the bottle to strip back myself. i will call them tomoz as its rcd protected table 41.5 inregs book allows the max zs not exceed 1667ohms. im in a bit of a rock and hard place

Although the current Ze is above the max of 0.8 ohms for a TNS supply the fact that all of your circuits have 30 ma RCD protection ensures your new installation is safe until WPD come back. I'm sure the assessor wouldn't know that the existing main earth connection isn't an official DNO one and just explain you've informed WPD of the issue and they'll be sorting it out soon. Honestly I don't think you need worry as you've identified the issue and are demonstrating that you've dealt with it correctly.
 
Well clamping into a gas pipe is real risk aswell. Come on you not gonna use an impact to do it.
and your not going to sweat a bond onto the gas pipe with a blowtorch., unless you're a plumber
 

Reply to Nic Eic Assessment When Dno Haven't Been To Replace Earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I have my nic assessment on the 27th of this month its been a few years since we have had one due to covid and being to busy and our...
Replies
3
Views
901
I have come across what I think is a looped supply - like a normal incomer but two of them coming up side by side. It's a TN-S arrangement with an...
Replies
12
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi all, I hope you can help me please. I had solar system installed nearly 2 months ago and my installer turned out to be cowboy despite having...
Replies
14
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock