    Hi All,
    I recently replaced an old rewirable fuse board for metal split load rcd board. However on testing prior to replacement I noted that one of the lighting circuits doesn’t have a cpc. I’ve put this in the EIC for the new board that no cpc for lights, advised client that needs rewiring and advise against metal fittings accessories etc,is this the right course of action to take? They do already have metal fittings on this circuit, Is rcd protection enough to cover this? Also the kitchen ring has no continuity on the neutral conductor, I’ve had all the accessories off to find it but can’t, I’m assuming the break maybe in a buried joint box as the kitchen is an old extension. What’s the best course of action to take regarding this please?
    Thanks
     
    • Dislike Dislike x 1
  2. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    You should at the very least removed the metal fittings before energising the circuit after the board swap. You have now left a potentially dangerous situation live and provided a certificate for it.

    Likewise with the broken neutral conductor, this should have been rectified before being energised.
     
    • Agree Agree x 9
    • Like Like x 1
  3. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    If you have replaced a consumer unit you should know the answers to those questions!
    An RCD is not considered as a catch-all, get you out of jail card. The client should not have any metal fittings in that circuit.

    Re the ring. You should identify where the break is and split the ring into two radials with a 20A MCB on each radial. Or identify between which two sockets the break has occurred and run a new length of cable bypassing the problem.

    Yes I know, I live in an ideal world …
     
    • Agree Agree x 4
    • Like Like x 3
  4. DPG
    Offline

    DPG Electrician's Arms

    Location:
    S Yorkshire
    Agree with above - you can't leave things as they are. And you haven't issued a satisfactory EIC. The installation is not safe, and your name is on the paperwork unfortunately.
     
    • Agree Agree x 6
    Last edited: Jun 4, 2018
  5. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Muzza115 you have replaced the CU correct? I would have tested prior to changing the board, any faults found, that couldn't be fixed easlily, then report to the customer that you can't change the board until the wiring faults have been rectified, charge for your time so far. Well that's what I would do, looks like your mistake was to swap the board anyway, imo. See DPGs post
     
    • Agree Agree x 5
    • Like Like x 2
  6. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    agree with above posts.faults should be found and rectified before changing CU. problem is customer won't want to pay. get jack the lad from the local pub to bodge it. as long as it works, who cares.
     
    • Like Like x 1
  7. Muzza115
    Offline

    Muzza115 Active EF Member

    Location:
    Buckinghamshire
    Thanks for the advice guys.
     
    • Like Like x 1
  8. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Your Welcome
     
    • Bad Spelling Bad Spelling x 2
  9. elsparko
    Offline

    elsparko Regular EF Member

    Location:
    scotland
    the police are on their way to get you
     
    • Funny Funny x 3
  10. Muzza115
    Offline

    Muzza115 Active EF Member

    Location:
    Buckinghamshire
    I have noted on the EIC that these need rectifying. And the client is a family friend who will listen to my advice. I was also going to use this job to show NICEIC inspector for domestic installer, as is the only one close enough that fits the criteria Would you advise that I do these remedials before the inspection, will he out right tell me to do one or accredit me once I prove the remedials are done? Thanks
     
  11. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    This matters not. You can't just not comply with the regs and say you informed the customer, and it's up to them to book rectifications in.
     
    • Like Like x 2
  12. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Not sure Muzza what the assessor will say, but posts 4, 5 and 6 say it all. Like I said your mistake was to swap the board in the first place without recyifying the faults, may be if you explaine your error you could get lucky, sorry Mate just sying like it is. Good luck anyway.
     
    • Agree Agree x 1
  13. ferg
    Offline

    ferg Electrician's Arms

    Location:
    N.W.Scotland
    I hope you have thick skin. You will need it.
     
  14. Muzza115
    Offline

    Muzza115 Active EF Member

    Location:
    Buckinghamshire
    I kind of expected to be torn a new one. The assessment is this Saturday. I’ll try and get it sorted this week. Thanks
     
  15. elsparko
    Offline

    elsparko Regular EF Member

    Location:
    scotland
    too late, youre going to jail

    main-qimg-57230a16c2dd13401881614523b25690-c.jpg
     
    • Funny Funny x 3
Loading...
Similar Threads - lighting neutral continuity Forum Date
Domestic Lighting circuit through airing cupboard DIY Electrical Forum Monday at 3:21 PM
Streetlighting for first time Electrical Forum Friday at 6:43 PM

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job