Hi just thought I'd throw this out here for a bit of light entertainment after the @Marvo thread (phew!)
So brother in law asked me to look at EICR which returned unsatisfactory. I have not looked at the installation to ascertain as to Class 1 or 2 fittings in the premises are installed. The bonding seems ok but is not verified on the water which is strange it got a tick. Or seen the DB so can't comment as yet. But there are a few things that are questionable like time for disconnection and C1 for no cpc. Also the box ticked there are no items adversely affecting electrical safety! Would be fascinating to know how he got the PFC considering Ze is .35 and PFC is 1.8Ka. Wondered what your thoughts are. Can't wait to have a look will post some piccys. Not to worry though he is NICEIC approved contractorIMG_3398.JPG IMG_3397.JPG . He/They did not want to remove lamps to test L-N IR again odd.
 
Hi just thought I'd throw this out here for a bit of light entertainment after the @Marvo thread (phew!)
So brother in law asked me to look at EICR which returned unsatisfactory. I have not looked at the installation to ascertain as to Class 1 or 2 fittings in the premises are installed. The bonding seems ok but is not verified on the water which is strange it got a tick. Or seen the DB so can't comment as yet. But there are a few things that are questionable like time for disconnection and C1 for no cpc. Also the box ticked there are no items adversely affecting electrical safety! Would be fascinating to know how he got the PFC considering Ze is .35 and PFC is 1.8Ka. Wondered what your thoughts are. Can't wait to have a look will post some piccys. Not to worry though he is NICEIC approved contractorView attachment 38236 View attachment 38237 . He/They did not want to remove lamps to test L-N IR again odd.
PFC could be 1.8KA due to bonding. Obviously PFC is tested with the main earthing conductor connected. The bonding could be causing a lower impedance and the lower the impedance the higher the fault current.
 
PFC could be 1.8KA due to bonding. Obviously PFC is tested with the main earthing conductor connected. The bonding could be causing a lower impedance and the lower the impedance the higher the fault current.
Bonding would help, but to get from 0.35 Ohms to the PFC required 240/1800 = 0.133 Ohms (say) the bonding would need to be about 0.22 Ohms by its good self . Which beats my best TT by a bit, I'm just jealous.
 
Bonding would help, but to get from 0.35 Ohms to the PFC required 240/1800 = 0.133 Ohms (say) the bonding would need to be about 0.22 Ohms by its good self . Which beats my best TT by a bit, I'm just jealous.
Did you ever see that thread on here where a member achieved a Ra <1 ohm....Think
It cost the company he was doing It for around 4K. IIRC there were multiple rods on top of each other on the corners of the building and a bare copper tape or similar exothermic welded to the rods. I can't seem to find the thread or even the member who posted it.
 
Rewire, its 50 years old. If I could get rewired I would. Stop worrying about 1.8 that 2.2 that, the cable is past its use by date by 30 years. I'd code defcon 1.
95% of the wiring in my house is 47 years old all tests out fine, in fact doing a bit of alteration tomorrow with the upstairs lighting with my obsolete black and red T&E.
 

Reply to No cpc to lighting circuit, no rcd protection 50 year old wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock