  1. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Im sure this has probably been asked before in this forum but ive just upgraded a fuseboard today and found no earth in the lighting (two core). Obviously the next thing to do would be to tell the customer either rewire or change everything on that circuit to class 2 fittings and accessories, but in this case the customer didnt want to go ahead with either.... what should i do? Cutting the circuit out would be abit extreme?
     
  2. peterhyper
    Offline

    peterhyper Regular EF Member

    Location:
    London
    Absolutely nothing you can do. As long as you have a clear record of what you have informed the customer and stuck a warning on their consumer unit (i always take a picture when I've done it) and if they choose to not have a rewire and keep their lovely metal light switches and fittings then that's up to them.
     
    • Like Like x 2
    • Agree Agree x 2
  3. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Is the circuit RCD protected?
     
  4. snowhead
    Offline

    snowhead Respected Member

    Location:
    Mildlands
    • Like Like x 3
    • Agree Agree x 2
    • Informative Informative x 1
  5. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    You've placed a circuit in service that has no cpc from origin?
     
  6. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Thats what i thought but what warning label can i use? Only found no provisions for earth do not replace insulated light fitting and accessories with metal ones. But that doesn’t really make sense seeings as they are already metal!
     
  7. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Yes it is! All the circuits are....
     
  8. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Yep... would you of left them with no lights?
     
  9. Andy78
    Offline

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    Rather than energising a circuit with no earth and connected metal fittings ? Hard to say, what does your risk assessment say ?

    Basically you've dropped a bollock and should have checked before the CU change and given the customer options at that stage.
     
    • Agree Agree x 10
  10. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    That’s the label you should use.
    If they ignore the advice, that’s their look out.
     
    • Like Like x 3
  11. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Come on you cant tell me you drop every fitting in the house before a fuseboard change???
     
  12. Elliott96
    Offline

    Elliott96 Active EF Member

    Location:
    London
    Cheers! So should i put it on the cert as a departure, put the sticker on and get out?
     
  13. Andy78
    Offline

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    I make an assessment of the system at the quoting stage and quote accordingly. This evening I dropped 8 light switches because a homebuyer survey had flagged up the possibility of no cpc on the lights.
    The regs require you to make sure the system is suitable for the alteration before you do the work. Fundamental principles.
     
    • Agree Agree x 4
    • Like Like x 3
  14. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    I have a customer who has no CPC on their lighting.
    Thought she’d change the plastic switches for some brushed stainless steel ones.
    Told me she’d earthed it.
    What she did, is put a fly lead from the back box to the face plate.
     
    • Funny Funny x 6
  15. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    You have a serious problem here. You have replaced a consumer unit and energised a circuit which does not incorporate a cpc which supplies class I fittings. It is not a departure and there is no notice you can put in place which is supported by BS7671.
     
    • Agree Agree x 9
    • Winner Winner x 1
    • Informative Informative x 1
Loading...
Similar Threads - earth lighting circuit Forum Date
No earthing on lighting circuit Electrical Forum Jan 14, 2019