Hi all, I've been asked to make an old 4 story townhouse "safe" and issue cert for renting out.
Hasn't been touched for so long it has bakerlite accessories with wood backing!
Straight away I'm seeing replace all accessories, replace CU, upgrade earthing. The wiring is all in PVC cables but typical no earthing on lighting circuits.
I hear you all scream "REWIRE"!
Problem is property is highly decorated and furnished and owners would rather not go down that route.
My question is, if I fit all plastic accessories throughout, and clearly state on CU and cert NOT to fit any metallic fittings. Can I get away with that?
Just asking as whenever I've come across this problem in past, I've always rewired lighting so bit unsure what complies.
By the way, I've done quick IR, ring loop tests, Ze etc and all ok, but how do you R1+R2 lighting with no earth?
 
you can do that, but obviously no R1+R2 on lights, and ensure that all switch faceplate screws are either into nylon lugs or covered with some form of insulating material. ( the plastic push in caps would probably suffice).
 
Hi all, I've been asked to make an old 4 story townhouse "safe" and issue cert for renting out.
Hasn't been touched for so long it has bakerlite accessories with wood backing!
Straight away I'm seeing replace all accessories, replace CU, upgrade earthing. The wiring is all in PVC cables but typical no earthing on lighting circuits.
I hear you all scream "REWIRE"!
Problem is property is highly decorated and furnished and owners would rather not go down that route.
My question is, if I fit all plastic accessories throughout, and clearly state on CU and cert NOT to fit any metallic fittings. Can I get away with that?
Just asking as whenever I've come across this problem in past, I've always rewired lighting so bit unsure what complies.
By the way, I've done quick IR, ring loop tests, Ze etc and all ok, but how do you R1+R2 lighting with no earth?
When you say the LL asked you to make safe, I feel your only option would be to carry out an EICR report your findings on an EICR Certificate and pass it to the Landlord, not done anything with rental properties, but I think there are special arrangement for certifying Rental Properties, there will be other Electricians on this forum who do this sort of thing as their main service, if you're not desperate hang on till one picks up on this post.
 
When you say the LL asked you to make safe, I feel your only option would be to carry out an EICR report your findings on an EICR Certificate and pass it to the Landlord, not done anything with rental properties, but I think there are special arrangement for certifying Rental Properties, there will be other Electricians on this forum who do this sort of thing as their main service, if you're not desperate hang on till one picks up on this post.
Ferg has sent you a good starting point.
 
damn. so my granddad ain't got his lamp lighting job back. he's turning in his grave ( that disturbed earth bottom the garden where my grandma put him and got his pension for 25 years before the dwp twigged).
 
I'm not a fan of the class 2 and label bodge. I would recommend a rewire every time and have walked away from some that don't want to.
Indeed such an approach is not actually recognised by BS7671 - I bet no-one can find the wording of any such label within any Edition of the Wiring Regulations.
 
We don't touch jobs like this, rectify or walk away. I am also of the belief a plastic light switch is not double insulated even with non conductive fixing screws, it is a plastic light switch.
 
Common sense needs to prevail. To say to a customer it is either complete re-wire and thousands of pounds worth of decorating or nothing is a little silly in my book.

There is nothing wrong with fitting plastic accessories. Remember you are not changing the circuit so you do not have to bring it up to current Standards. That said if there is nothing wrong with the existing switxhes why change them at all?

When wired it was completely acceptable to install plastic accessories and not have an earth on the circuit. If an EICR was carries out today with only plastic fittings installed it would only warrent a C3 so that in itself suggests it is not dangerous.
 
Not sure what the relevance is unless the op was suggesting a re-wire with no cpc.

I'll be honest, I'm not entirely sure of the relevance either, but I took it to suggest that the method of using class 2 accessories, mentioned in the same section, should not be employed in a domestic situation. Otherwise what would be the point of putting it in the guide to consumer unit changes ?

If we are to ascertain that all existing equipment is safe for the alteration before work commences (132.6),
and if 412.1.3 deems that the method of double insulation is not to employed in a domestic situation, then we cannot fulfil our obligation to the requirements of 132.16 if it is employed.
 
Interesting points from both sides of the argument but I can’t see how you can class something as potentially dangerous if plastic accessories are fitted throughout the lighting circuit(s).
On the other hand an unearthed back box tho not necessarily accessible to touch could become live through breakdown of the insulation and if the homeowner was to decorate the wall then the added influence of water could have dire consequences.
Yet as stated there’s no law to say an installation must be upgraded to current standards.
The obvious problems start when we alter the circuit and installation and we need to comply with 132.16.
What I do know is, it does seem to be an acceptable practice in the industry to label the DB and have only plastic accessories throughout the circuit
Think I need a lie down
o_O
 
Indeed such an approach is not actually recognised by BS7671 - I bet no-one can find the wording of any such label within any Edition of the Wiring Regulations.
There’s a requirement to provide labelling at the DB for circuits with high protective conductor currents but no such label exists in bs7671 so it’s a similar situation label wise I mean.
The label for protective currents above 10mA is required by bs7671 in section 543 and is mentioned so perhaps that is indeed the big difference between the 2.
Often labels required are not actually in the wiring regulations themselves.
 

Reply to No earthing on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
834
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock