Discuss no evidence of supplementary bonding to pipe work in the UK Electrical Forum area at ElectriciansForums.net

E

egginyourface

I went and did a visual inspection on a flat. No Rcd protection present.

10 mm earth to water and gas was connected.

No sign of supplementary bonding. So i did a long lead test and found that all pipe work in kitchen and bathroom was below 0.05 Ω.

Does this mean no supplementary bonding is required?

Ive advised the board be upgraded but dont think they can afford it
 
I would not worry about the kitchen as its not required under BS7671.

In addition to reg 701 and doubt exits re the effectiveness have a look at reg 415.2.2 but you will need to do some testing to establish if it is connected in the bathroom!

Hope this helps!
 
Yes then supplementary bonding may be omitted as long as the 3 conditions are met as per 701.414.2.

This is where the Visual Inspections are worth nothing IMO as the only way you can establish the above is by getting you test equipment out!
 

Reply to no evidence of supplementary bonding to pipe work in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, has anyone got any experience of resistances through press fit plumbing fittings? Just been to a job I did last year which was a...
Replies
8
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always...
Replies
36
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock