Hi guys, cannot get a resistance reading when using my Robin loop tester. It just shows 204v and the red do not proceed lamp lit.
Never come across this before any ideas would be appreciated. (The live neutral reading is 243v)
New rod fitted and driven in to good ground at about 2.3 meters.
 
Where is the installation? Can you see the supply transformer? Is the rod in good ground ie not made up/ back fill. Out of interest is the old rod still in place could you test that for reference. Have you in stalled a new earth conductor or reusing existing? If you are testing remote of the rod then what earth continuity reading did you get ?
 
Hi - only basic thoughts, sorry - confirm rod actually connected to met (wander lead). Confirm tester (test at another site, check batteries). My KT65 measured a TT earth loop over 300 Ohms last week, it was corrosion at the rod to cable connection, thankfully :) .
 
Could be like mine was today o_O
A5BA563D-1A8E-416C-9DFF-AC377188FFCC.jpeg
 
I can see the supply tranny and the rod is new and gone in very good ground. The old rod was giving the same problem so cant use that as a reference. Just never had this before. My only thing i can perhaps think of is volts drop but line to neutral reading comes up as 243v so no problem there.
 
If you are attempting to measure the resistance of the electrode that connects to a generator you need an earth electrode tester as the rod will be referencing the generator neutral to earth.
Attempting to use an earth fault loop impedance tester will not work as the electrode doesn’t form part of the earth fault loop impedance path.
Either that or I have misunderstood your post.
 
As in #7 have you done a continuity test of the earthing conductor to the electrode.
What Robin tester is it.
 
That tester will measure up to 2000 ohm and it is unusual to get a do not proceed indicator unless polarity is incorrect or you have an almost non existent earth, I use one day in day out.
 
Barring any inaccuracies to the measurement I guess the soil resistivity could be very, very poor?

Could you try connecting the new rod to the old to see if that improves the Ra?

Also, could you try an RCD trip test on the RCD? If it trips then you know your measurement of 207V is incorrect and therefore not being measured accurately (as I dont think the RCD would trip if only 207 V L-E). Not sure about this last paragraph though! Just a thought.
 
Barring any inaccuracies to the measurement I guess the soil resistivity could be very, very poor?

Could you try connecting the new rod to the old to see if that improves the Ra?

Also, could you try an RCD trip test on the RCD? If it trips then you know your measurement of 207V is incorrect and therefore not being measured accurately (as I dont think the RCD would trip if only 207 V L-E). Not sure about this last paragraph though! Just a thought.
 
Just to update on this problem. I thought i would walk down the road to the cottage next door to ask if i could plug my loop tester in a socket to see what reading i got and low and behold it read 201v. So looks like transformer problem, as got talking to them and they said they lost power earlier in the year due to lightning. WPD sending someone to look at transformer.
 
Just to update on this problem. I thought i would walk down the road to the cottage next door to ask if i could plug my loop tester in a socket to see what reading i got and low and behold it read 201v. So looks like transformer problem, as got talking to them and they said they lost power earlier in the year due to lightning. WPD sending someone to look at transformer.
 

Reply to No ze at origin of tt system in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
933
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock