hi guys
For any of you that carry out periodic emergency light testing on HMOs.
I have read through bs5266 but want to get your perspective on these issues and if you would fail the system
There are non maintained emergency lights fitted to each floor and landing so the siting of the lighting is sufficient but they have not fitted any key switch facility. They have basically wired off the existing circuit in a couple properties so you do have to isolate the circuit and all normal supply lighting to that floor to test the emergency light.
Although in one property they have wired a seperate circuit just for the emergency lights not connected to the existing lighting circuits, surely this fails based on the fact that if normal supply lighting was to trip the emergency lights would not kick in only unless there was a power cut.

Sorry for the long text guys but want your opinions on what constitute a fail when carrying out your emergency light testing.
 
While not having a test switch is a non-conformity, I would prefer to switch off the normal lights when testing, as it allows me to gauge whether the EM lights provide sufficient light for their purpose.
Having the EM lighting on a separate circuit to the normal lighting is a bit pointless.
I would just wire that circuit in with the normal lighting circuit it is designed to work with.
 
See Annex K of BS5266:1. This gives a certificate for verifying an existing installation which is essentially a tick list with areas to list any non compliance and recommendations. If the fittings are maintained then they do not have to operate with the general lighting circuits.
 
A fuse or an MCB is perfectly acceptable to be utilised as a test facility so long as it is suitable. I am certain in a HMO this would be fine.

In respect to emergency lights not energising when the local lighting fails this is certainly a non-conformity.
 
While not having a test switch is a non-conformity, I would prefer to switch off the normal lights when testing, as it allows me to gauge whether the EM lights provide sufficient light for their purpose.
Having the EM lighting on a separate circuit to the normal lighting is a bit pointless.
I would just wire that circuit in with the normal lighting circuit it is designed to work with.

An OCPD is classed as a test switch.
 

Reply to Non conformities when doing emergency light testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
566
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
809
Hi, RCBO appropriate test facility for emergency lighting? I have a car storage facility ( one corridor with 10 rooms off the corridor to store...
Replies
12
Views
1K
Hi all Got a question regarding HMO compliance. Visited property today for landlord looking to apply for an HMO license for one of their...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock