Discuss Non-fused spur on A2 Radial Cct ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

marshr02

Can someone help me?

Section 8.2.4 spurs - 17th OSG
---------------------------------
"In ... an A2 radial cct of Table8A a non-fused spur should feed only one single or........."

I was under the impression that spurs only existed on ring ccts i.e they are a 'radial' tap off the ring.

I was intending on installing a 32A, 4.0/2.5 radial circuit. I was expecting to be able to 'branch' the radial cct early on to suit the house layout. Is one branch the radial continued and the other branch deemed a spur and limited to one socket?

I don't see the issue provided the total cable length to each 'leg' of the radial circuit in within spec, hence Zs is within spec. Obviously the 4mm cable is protected by the 32A MCB.

Any help, greatfully appreciated.


- Is the definition of a spur a later addition to an existing circuit?
- Is the definition of a spur a branch off a ring circuit?
 
Last edited by a moderator:
If you have the 17th Edition Regs book - Appendix 15 gives examples of both Ring and Radial Circuit arrangemnets.

However I do believe that there is an update to it so use your logic.
 
Sorry - my boss wont pay for us to get the A4 Red Book - so only have the OSG at the mo. I'll go looking for the chapter you mention - when I get access to a book.

Cheers

.
.
..
.
.
.
I suspect the answer if because the A1..3 circuits are purposely a general solution for most houses. The limits & contraints on no. of spurs etc are to keep well within all the usual specs; volt drop, Zs, etc, loading, diversity.

If a sparky is happy to ignore 'standard circuits' he is free to design what he wants providing he meets in the design stage all the standard specs?

I'm looking for an experienced sparky to put me out of my misery on this - I've little experience, freshly qualified. Cheers
.
.
.
.

Thanks WarrenG - spot on.

Just googled the IET for the errata info for Appendix 15 - they publish this free. It shows exactly what I want.

For those interested in the answer. A 4.0/2.5 32A radial circuit can branch provided cable stays 4.0/2.5. Spurs are 2.5/1.5 - one per.
 
Last edited by a moderator:
Spurs, unfused off a ring to feed only one socket. If fused put as many sockets on the spur as you want. (Obviously the fuse will protect it if you try to overload it)
You can put a spur straight out of the CU on the same terminals as a ring circuit also...this is counted as a spur off the ring, but gives you a lot of freedom compared to running one out of a socket on a ring...maybe this will suit your needs better?
 
Thanks for reply Randyrat. I feel fine in terms of understanding spurs on ring circuits - just a bit confused re radial. WarrenG's post sorted me out.

Cheers Guys
 
Thanks for reply Randyrat. I feel fine in terms of understanding spurs on ring circuits - just a bit confused re radial. WarrenG's post sorted me out.

Cheers Guys

marsh02,

Not sure which info you managed to get but there were some updates to Appendix 15 which are here. Just for your reference.

http://www.------.org/publishing/wi...es/bs7671-2008-corrigendum-jul08.cfm?type=pdf
 

Reply to Non-fused spur on A2 Radial Cct ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
834
I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock