Zdb

-
Esteemed
Reaction score
496
If for whatever reason you can't do an R1+R2 test on a ring final circuit (unable to identify opposite legs). There's also an option on the paperwork for the R2 value...

Am I correct in thinking that you do an end to end test on the CPC's which would give you r2, then just divide it by 4 to give you R2?
 
If for whatever reason you can't do an R1+R2 test on a ring final circuit (unable to identify opposite legs). There's also an option on the paperwork for the R2 value...

Am I correct in thinking that you do an end to end test on the CPC's which would give you r2, then just divide it by 4 to give you R2?
Yes but what about your continuity tests end to ends on the ring final?
If it's periodic testing then just take the zs at each socket.
If it's initial verification then continuity needs to be established/verified so R1+R2 shouldn't be an issue.
 
no because you will not have cross connected and tested the RFC correctly, why the difficulty in identifying the RFC legs?
 
I did continuity of L, N & E at the D.B. I just didn't want to leave a box blank.
 
Edit But yeah doing end to end on live and cpcs added and divide by 4 should give you total value of R1+R2 as you have 2 middles which can be considered the end of the circuit if it was a radial and 2 conductors in parallel
 
Following on from the above question consider a situation where you can't readily disconnect the cpc at any point to test it, or doing so is rendered largely pointless by the installation method.

I'm thinking of a circuit wired in SWA, MICC or steel conduit/trunking.
 
Following on from the above question consider a situation where you can't readily disconnect the cpc at any point to test it, or doing so is rendered largely pointless by the installation method.

I'm thinking of a circuit wired in SWA, MICC or steel conduit/trunking.
Yes R1+R2 really only works in an all insulated wiring system I guess.
Method 2 is usually used for conduit systems
 

Reply to Obtaining R2 value on RFC in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock