If it’s the solution it’s the solution ......

Why do you say it’s price prohibitive

If the customer won’t pay to do it properly , just walk away

I wish, I'm asked to make it work and given a spend limit. Running three new circuits is above that.

Not ideal is not necessarily non-compliant.
 
I know but there already there with the flexes run in so rather than have to patch the holes, just use them.

OK, consider this, 3kW at 240v is 12.5 amps. Your voltage may be above this at 245v so 12.76 amps. If the immersions are rated at 3kW at 230 volts we would have 13.04 amps at 230v or 13.6 amps at 240v, 13.9 amps at 245v. Don't forget the voltage is allowed to rise to 253v.

Anyway the 13 amp fuses are going to run hot at these sort of continuous loads with subsequent damage to the FCUs.
 
OK, consider this, 3kW at 240v is 12.5 amps. Your voltage may be above this at 245v so 12.76 amps. If the immersions are rated at 3kW at 230 volts we would have 13.04 amps at 230v or 13.6 amps at 240v, 13.9 amps at 245v. Don't forget the voltage is allowed to rise to 253v.

Anyway the 13 amp fuses are going to run hot at these sort of continuous loads with subsequent damage to the FCUs.

Is that maths right? should the Amps drop as the Volts rise?


Again, not disagreeing with you in principle but the same could be said for any Immersion connected via an FCU.
 
I'd be very surprised if bs1363 doesn't take into account permitted variations in the supply voltage.

That said, I always put immersions on a 16A breaker and a DP switch.

For some reason I tend to wire the circuit in 2.5 as well, even though I keep telling myself 1.5 would be fine!
 

Reply to odd one seen today, three FCUs each for a 3KW immersion on one 6mm radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello - Looking for assistance regarding a problem with my three way switch what was working over the past four months with no problems until this...
Replies
0
Views
694
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock