    Hi guys could I get some advice?

    I went to a customers house to change a thermostat in a thermal store (Gledhill pulsacoil 3) and the spur was labelled "off peak water heater".

    I isolated supply and replaced stat. However it appears to have a live supply all the time? I used a clamp meter and it is drawing 13 amps. This was around 1pm.

    Her consumer unit has a little indicator that flicks from black to red when it is off peak. Could this mean that she always has power to heater but it is cheaper to use at night? Just trying to get her an answer if any of you know?
     
  2. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    With some economy setups you can manually override it and use outside the cheaper period but obviously it costs more. Examples being very cold weather where storage heaters are on max all day. It depends on the set up though. Most eco7 systems i see around here are dead as a dodo during the day and cant be over ridden. But like magic come on at night. Also just because the system is set up as a eco system doesnt mean it has not at some stage been altered with the night time cheaper cu being fed from the main daytime board or henley block on the tails possibly even bypassing the eco7 meter or radioswitch thingy.
     
    • Like Like x 1
  3. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    Business Name:
    David Haddock Electronic Repairs
    Have you checked the wiring at the CU and /or tariff switch ?
    Does it look like it has been altered ?
     
  4. mrlennie
    Offline

    mrlennie EF Member

    Location:
    Manchester
    Hiya I have not. I am a humble plumber and was just wondering if it was a common occurrence that I have not happened upon.

    The meter had 2 reading and both are going up the customer says so I assume the economy 7 is wired up and not completely bypassed?

    My next thought is to say to her to put immersion on at night and see what the readings say in the morning. If economy 7 reading goes up then it must be able to be used during the day and then goes to off peak when programmed to.
     
  5. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    I think some of those systems have a 24/7 supply ............ so is it wired and switched properly?

    Was there another 13A supply close to the one you switched off?
     
    • Like Like x 1
  6. littlespark
    Online

    littlespark Electrician's Arms

    Location:
    Scottish Borders
    Some suppliers have different off peak systems. Economy 7 as everyone knows... Economy 10 which gives everything a boost through the day and Economy 2000.
    That's Scottish Power's invention.

    Some E7 systems have a boost programmer, so you can turn on the immersion during the day. (grey box, bigger than a double socket with a white dial) Maybe this is kaput and on all the time
     
    • Agree Agree x 1
  7. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Agree checking if its Economy 10 or similar, in the first instance. Ones I've worked have an on period in the afternoon, early evening but shorter overnight period. Ask your client to check with their fuel supplier.
     
  8. mrlennie
    Offline

    mrlennie EF Member

    Location:
    Manchester
    Great thanks so much for your suggestions. She does have a boost for the top immersion wired right next to this one.

    Just this business of her CU having a little RCD style black / red indicator for eco 7 which I found odd.

    Thanks again everyone. Will update when I know more.
     
    • Like Like x 1
  9. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Op, if you do a few more posts you will be able to upload pictures
     
    • Like Like x 1
  10. Timbo
    Offline

    Timbo Regular EF Member

    Location:
    Sussex
    Business Name:
    TechFix Services
    Is it fed from the main consumer unit or is there a separate Economy 7 one?
     
    • Agree Agree x 1
  11. Percyprod
    Offline

    Percyprod Regular EF Member

    Location:
    Cumbria
    Some off peak systems still have mechanical time switches, and although they have either a clockwork or battery back up to take over in the event of a power cut, it doesn't always work, so when the power comes back on the clock is at the wrong time.
     
    • Like Like x 1
  12. Dave OCD
    Offline

    Dave OCD Forum Mentor

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    And just recently I've worked in a bungalow built around 1968 for new owners and the old mechanical timeclock hasn't budged from 1.30am over a 3 week period. [Various visits]. Needless to say the customer has advised her supplier. :)
     
  13. mrlennie
    Offline

    mrlennie EF Member

    Location:
    Manchester
  14. mrlennie
    Offline

    mrlennie EF Member

    Location:
    Manchester
    Have managed it :)
    The little box on the bottom left where the MCB would have been is where the indicator is - it's really small. Little black ( or red when off peak ) box next to the "ATON" mark.
     
  15. Timbo
    Offline

    Timbo Regular EF Member

    Location:
    Sussex
    Business Name:
    TechFix Services
    That is a 4 pole contactor which presumably switches the outputs of the 3 heater mcbs and should also do the off peak water heater.

    Do the heaters work as they should - i.e. come on over night?

    Is there a timeclock any where nearby to control the contactor? The mcb top left is marked as contactor.
     
    • Like Like x 1
Loading...
Similar Threads - peak immersion working Forum Date
Lady not speaking to me Electrical Forum Dec 31, 2018
Domestic Ceiling speakers in cold deck roof. Electrical Wiring, Theories and Regulations Dec 18, 2018

Share This Page

Users found this page by searching for:

  1. off peak power during day

    ,
  2. immersion heater off peak switch

Electricians Directory Post a Domestic Job Post a Commercial Job