Hi all, searched the forum for any info on this but to no avail...

I have been installing PV systems for ages now, and have been connecting the AC cable to an MCB on the RCD side of the consumer unit whenever there is a spare way..
I spoke to another installer and he told me that this cant be done, the cable must be connected to an MCB an RCD protected garage unit which is fed via tails taken from the main switch or link boxes, because under fault conditions if the RCD trips the inverter will still be producing power for up to 5 minutes, and the busbar (and circuits) will still be live.

A way to get round this is to install an RCBO in the consumer unit, but there is not always a spare way on the non-RCD side...

Dont the inverters have a shut-off built in in the absence of an AC input?

Can anyone shed any light on this?

Cheers!
 
Hi all, searched the forum for any info on this but to no avail...

I have been installing PV systems for ages now, and have been connecting the AC cable to an MCB on the RCD side of the consumer unit whenever there is a spare way..
I spoke to another installer and he told me that this cant be done, the cable must be connected to an MCB an RCD protected garage unit which is fed via tails taken from the main switch or link boxes, because under fault conditions if the RCD trips the inverter will still be producing power for up to 5 minutes, and the busbar (and circuits) will still be live.

A way to get round this is to install an RCBO in the consumer unit, but there is not always a spare way on the non-RCD side...

Dont the inverters have a shut-off built in in the absence of an AC input?

Can anyone shed any light on this?

Cheers!

Inverter will stay on for a max of 5 seconds (not 5 minutes),.

Whichever way you look at it you need to put the MCB on a circuit that does not share an RCD with other circuits that require a 0.4 second disconnection time. Some choices are:

Connect a seperate garage CU unit and use only one MCB from that CU (as you've been told)

If you've got a 17th Edition CU - have you got one that has 2 RCD busbars and another seperate busbar (can't remember how these circuits are referred to) - typical 17th Edition CU would be 2-4-4 for instance.

If you've got a 16th Edition board put the PV on the non RCD side.
 
Big question this one....

The inverter is only required to reduce touch voltage within 5 seconds and not 0.4 seconds. Undoubtably when testing the RCD serving your inverter you did not allow it to go back into generation mode before continuing with the RCD test. (1/2 x both side of sin wave, 1 x both sides and 5 x both sides) if in generation the 30mA RCD Probably will not trip within 0.4 seconds. If this RCD is also serving sockets outlets, shower or any other circuit requiring supplementary protection then by connecting the inverter it has created a potentially serious situation. There is nothing stopping you fitting a RCBO but again not on a shared RCD.

Now the question is over cables embedded in walls at less than 50mm. According to the regs a cable installed in this manner with no earthed mechanical protection requires 30mA protection. But again the inverter will not stop the RCD from tripping but the touch voltage could still be present for 5 seconds. There has been discussions on wether to fit a RCBO to both ends of the inverter AC supply (at inverter and at consumer unit) a reasonable but complicated and may be costly approach. We fit either SWA or not embed in walls.

Where a none RCD way is available we use it, where a small board is protected by an overall RCD we might replace this with a main switch and fit RCBO's to the required outgoing circuits and MCB to the PV. Where there is no option we will fit a two way board with main switch and a MCB solely for the PV.

There are no additional requirements under BS7671 that require PV to be on a 30mA RCD other than the standard requirements but even then it wouldn't work as it is designed to!

And so the argument will continue...............
 
Big question this one....

The inverter is only required to reduce touch voltage within 5 seconds and not 0.4 seconds. Undoubtably when testing the RCD serving your inverter you did not allow it to go back into generation mode before continuing with the RCD test. (1/2 x both side of sin wave, 1 x both sides and 5 x both sides) if in generation the 30mA RCD Probably will not trip within 0.4 seconds. If this RCD is also serving sockets outlets, shower or any other circuit requiring supplementary protection then by connecting the inverter it has created a potentially serious situation. There is nothing stopping you fitting a RCBO but again not on a shared RCD.

Now the question is over cables embedded in walls at less than 50mm. According to the regs a cable installed in this manner with no earthed mechanical protection requires 30mA protection. But again the inverter will not stop the RCD from tripping but the touch voltage could still be present for 5 seconds. There has been discussions on wether to fit a RCBO to both ends of the inverter AC supply (at inverter and at consumer unit) a reasonable but complicated and may be costly approach. We fit either SWA or not embed in walls.

Where a none RCD way is available we use it, where a small board is protected by an overall RCD we might replace this with a main switch and fit RCBO's to the required outgoing circuits and MCB to the PV. Where there is no option we will fit a two way board with main switch and a MCB solely for the PV.

There are no additional requirements under BS7671 that require PV to be on a 30mA RCD other than the standard requirements but even then it wouldn't work as it is designed to!

And so the argument will continue...............

If only more companies did this, I have come across pv on single
Rcd boards four times in 2 months on condition reports, and yes it takes about 5secs to loose potential, from what I've seen.
Could be rather Dangerous!!
Thanks for the post.
Hope People can see the Error
 
there is also a suggestion that if you do need an RCD for reasons under 1771 then it should be a type B RCD (as against a type b MCB which is something entirely different), which are £2-300
 
If you need an RCD for other reasons (i.e. under 7671, such as on a TT supply) and the inverter doesn't have glvanic isolation then you need a type B RCD (712.411.3.2.1.2)
most inverter manufacturers specify 100ma RCD minimum
 

Reply to Ok to connect AC cable to MCB in Consumer Unit??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
655
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock