Hi there,

Let me start by saying that the picture is not my work! I regard myself as a reasonably competent DIY'er - probably as competent as one can reasonably be without any form of training.

Attached is a picture of my Consumer Unit, or fuse box. It looks... a bit... shall we say shabby? I haven't seen a lot of consumer units in my time, so maybe this is more normal than I thought, but to me it doesn't look like a professional job. I should point out I'm responsible for the missing fuse, I was trying to figure out where it went. It turns out that it went to a wire in the airing cupboard which, despite being wired to a live 30A fuse, wasn't even capped! I've taken care of that now, but is this consumer unit something I ought to get replaced?

Note I have read this: Do I need to update the fusebox in my house? - MyBuilder - https://www.mybuilder.com/questions/v/2384/do-i-need-to-update-the-fusebox-in-my-house

...which seems to suggest that replacing a fuse box just because it's old isn't necessary. Hence the pictures. So the question is - DO I NEED TO GET THIS FUSE BOX REPLACED?

View attachment DSC_0601.JPG
 
There is no reason why you "need" to update the fuseboard unless you plan changes to any of the circuits ....that said, you should plan to get it updated at some point.... Just on the basis of improved safety for you and your family.
 
It's a bit hard to tell from the picture but it looks like you might have some rubber cables still connected(possibly cooker?).These would need to be updated before you had a new consumer unit fitted.
 
It depends on how you define 'need' I guess.

If you want to know if there is any legal or regulatory requirement to replace it, then no you don't need to have it replaced.

If you want to make your home as electrically safe as possible and do the best you can to prevent you, or another member of your family from receiving a potentially fatal shock then I would say you need to get a competmat electrician to have a look and advise accordingly.

Having the consumer unit replaced, whilst being a good way to improve safety, may not be the most urgent upgrade if the wiring is not in good condition.
 
sad thing is that DB would have been pristine when installed. all cables dressed neatly, and circuits labelled. since then (1960's?) a succession of cowboys and DIYers have performed alterations with the most technical tool being a hammer.
 
What is the switch on the right of the picture for? It looks like a supply to another floor? So are you in a flat or house? Are you the owner. I worry about competent DIYers like yourself. You have removed a fuse and left everything on and open and I guess gone poking around with a neon screwdriver to find an exposed live in the airing cupboard, that has been "taken care of" how did you do that? And how do you know it is the wire in question?
 
Hi, thanks all for your responses.

Vortigern, you're right to worry about DIYers - a lot of us think we're competent and then end up burning the house down. To anwer your questions - the switch on the right is for a separate feed, which powers an electric shower. I haven't been, and won't be going anywhere near that.

I was trying to find out roughly where everything went, so I removed each fuse in turn - powered off at the main switch, removed one fuse, powered back on and went round the house to see what did and didn't work. Not a perfect system, but a good starting point, I figured. I took this photo during that experimentation phase, so I haven't left everything open. And I don't trust those neon screwdrivers, in my early DIY days I had a faulty one which nearly killed me - I use a multimeter, first using the NCV beeper to test whether I'm in the right neck of the woods, then use the AC voltage meter across live and neutral to see what is and isn't actually going on.

The wire in question has been "safely" capped off temporarily with a block connector and electrical tape, which has then been taped to the wall in the airing cupboard with a self-made "DANGER" label attached to it. My longer term plan was to remove this wire at the fuse box end and eventually remove it altogether as the floorboards come up. I was going to ask about that here, but in line with the above, I figured if I have to replace the whole box anyway I might as well do it then.

Since there are so many helpful people here, I'll draw up a schematic of where all the wires go from what I've figured out so far. You might find it entertaining, or maybe you'll tell me the things I find odd are actually normal practice for some reason.

If there is anything unsafe about anything I've written here, PLEASE tell me. I approach safety with a mixture of a tiny bit of industry knowledge, a whole heap of common sense, and a reasonable measure of overkill where I can, but I'm not a proud man, and I'd far rather be told I'm an idiot than kill myself.
 
If all you have done is remove the fuses then why have you taken the front cover off of the fuseboard?

A multimeter is not a safe method of proving whether a conductor is live or dead, they can give false readings for various reasons, one of which is capacitive coupling between conductors.
 
Hi @fishkake Ok so its a shower, I am going to guess the other answers; it is a house and you are the owner. Ok so it is ok for you to be poking around then. So the past couple of days I have removed and replaced our bathroom suite and...removed the electric shower. I have put in a thermo/mixer valve instead, why I hear you ask because I hate the idea of water electrics and me and mine underneath it all. And thats an electrician. Now...we have modern electrics with RCD protection so it should be safe yes? Hmm maybe but I still don't like it. You have the same as me but with one difference, no RCD. I would not even consider going under such a shower, gives me the shivers. Just superstitious me though. As for the rest appearances aren't everything it is a matter of ...what lies beneath! You can only find that out by professional inspection and some testing. I would suggest you commission an EICR of the mid price variety i.e. not sub ÂŁ100 not over ÂŁ250 which will give you a fair idea of what needs doing. Personally if it were my installation I would like to keep that vintage look and just do what is necessary to make things safe. I may put a separate RCD on the shower though. But of course that is me sort of eccentric, love the older things, rather like myself.
 
Sorry, I didn't answer that, but yes, it is a house and I own it. Technically, the bank still own about 72% of it. I too will be replacing the electric shower with a mixer and pump. Not far safety reasons, I just hate electric showers. My bathroom is currently in a dismantled state, and once I'm done with that the other supply with have no purpose. I want to use it to put a separate supply in my office to run some awesome (and power hungry) computer equipment, but that's for another day.

The EICR is a good idea. I'll be honest, if your ballpark is correct, that's cheaper than I thought, I will have a look in to that.

@davesparks - what tool should I be using? If you look here:

http://www.doityourself.com/stry/how-to-test-a-socket-with-an-electronic-multimeter

How to test an outlet with a digital multimeter | eHow UK - http://www.ehow.co.uk/how_5840711_test-electrical-outlet-digital-multimeter.html

Safe Meter Usage | Electrical Safety | Electronics Textbook - https://www.allaboutcircuits.com/textbook/direct-current/chpt-3/safe-meter-usage/

These all seem to think a multimeter is well suited. And this document: http://www.hse.gov.uk/pUbns/priced/gs38.pdf seems to think that my equipment needs to be CAT III or CAT IV rated, which my multimeter is.

I'm not trying to prove you wrong, just to make sure I know what I'm doing - if using a multimeter isn't safe, the internet is VERY misleading to this end. In fact the page for my multimeter basically lists it as a selling point.
 
Oh, @davesparks to answer your other question - because I'm an idiot :) I thought I had to take this off to remove the fuses. After removing the lid, a quick look at the exposed wires set off an alarm bell in my head that said "I really don't think you should be in here..."

You'd think it would have a label on it or something, but nope. Maybe a previous DIYer removed it!
 
You'd think it would have a label on it or something, but nope. Maybe a previous DIYer removed it!

They didn't have such labels in those days, the general public were expected to have some common sense and not need instructions and labels to save them from themselves.
 
Hi @fishkake safety with electrics is a big subject. When the system is old like yours there can be problems that are counter-intuitive when testing. For instance the Earth or the Neutral can be live in certain conditions. It is often the case DIY peeps do not know this and assume they can touch a neutral or earth with immunity. Not so...there is a specific way for testing of live involving all three wires which I am not about to hold a seminar on you will be relieved to hear. However I cannot emphasise enough caution when dealing with electrics. @davesparks was very likely referring to a double pole voltage tester compliant with GS38. Fluke T150 Voltage/Continuity Tester - https://www.tester.co.uk/fluke-t150-voltage-continuity-tester?fee=3&fep=5456&gclid=EAIaIQobChMI1uS_xPz31QIVxLztCh1NvQ2MEAQYAyABEgIQuPD_BwE
Sorry to steal your thunder @davesparks This and how to use it comprises a safe isolation procedure and there is more. Think long and hard before diving in too deep.
 
what type of service head is that chaps? looks wide enough for 2 fuses? ie one in the N? o_O? never come across one quite like that
 
what type of service head is that chaps? looks wide enough for 2 fuses? ie one in the N? o_O? never come across one quite like that

It's one of the early insulated cutouts, most likely to be a TNS service with a PILC service cable.

I'm not sure if they're are old enough to have had fused neutrals originally, but if they were then it should have been replaced with a solid link.
 
And this document: http://www.hse.gov.uk/pUbns/priced/gs38.pdf seems to think that my equipment needs to be CAT III or CAT IV rated, which my multimeter is.

And in the section SAFE SYSTEMS OF WORK;

19
Where a test is being made simply to establish the presence or absence of
voltage, a proprietary test lamp or 2-pole voltage detector suitable for the working voltage of the system should be used, rather than a multimeter.
The use of incorrectly set multimeters (or makeshift devices) for voltage detection has often caused accidents.

20
Any device used to prove dead may fail to indicate danger (eg a faulty lamp not indicating a live circuit). Such devices should be proved before and after use. This should be done preferably on a voltage proving unit (some devices have built-in proving units) or otherwise on a known live source of similar voltage to the circuit under test (providing precautions are taken to prevent danger arising).
 
:eek: I think OP your one of those DIY's whose like to go too far with things. Stop messing around with things, before you kill yourself or someone else. In ten years time you might not own this house, and put the new owners in danger.

So get some quotes from some competent qualified electricians, to have that CU replaced. And looking at the state of the cables, the property has subjected to other weekend warriors (no offence meant). Therefore I would be considering having it re-wired, but that bit is my personal opinion.

Edit; not withstanding the excellent previous advice given by members :)
 

Reply to Old Consumer Unit / Fuse Box in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
356
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
216
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
976
Hi, I am due EICR test on my property which has 20 year old wiring. Last test on 2018 was fine with no issues. Just need to check if my consumer...
Replies
4
Views
1K
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock