Paul D

-
Reaction score
0
Hi all,

Just joined this forum whilst doing research, so thought why not ask my question directly.

I am going to have a small split system aircon unit installed for my bedroom.

It will be a modern Mitsubishi unit with a starting current of only 3.5 Amps, nominal running current of 2.9 amps and absolute maximum running current of 7.3 Amps.

For convenience, I was intended to spur off a double socket in the bedroom straight through the wall and run 2.5mm T+E in plastic conduit down to where the outdoor unit will be.
(I know a dedicated supply would be preferable, but the Consumer Unit is the other side of the house)

I will install a 4 pole rotary isolator next to the aircon unit for maintenance isolation purposes.

Question: For this type of installation, do I need to install a Fused Connection Unit between the double socket and the rotary isolator?

Thanks in advance for any advice given.
 
it would be advantageous to install a double pole FCU as a means of isolation for maintenance or if the unit develops a fault.

if you're installing in conduit, why not use 2.5mm singles?
 
Hi all,

Just joined this forum whilst doing research, so thought why not ask my question directly.

I am going to have a small split system aircon unit installed for my bedroom.

It will be a modern Mitsubishi unit with a starting current of only 3.5 Amps, nominal running current of 2.9 amps and absolute maximum running current of 7.3 Amps.

For convenience, I was intended to spur off a double socket in the bedroom straight through the wall and run 2.5mm T+E in plastic conduit down to where the outdoor unit will be.
(I know a dedicated supply would be preferable, but the Consumer Unit is the other side of the house)

I will install a 4 pole rotary isolator next to the aircon unit for maintenance isolation purposes.

Question: For this type of installation, do I need to install a Fused Connection Unit between the double socket and the rotary isolator?

Thanks in advance for any advice given.
No because the Evaporator (indoor unit) is fed directly from the condenser (outdoor unit) You isolate the entire system for maintenance. Isolating the indoor unit only could cause damage to the outdoor unit.
 
Last edited:
it would be advantageous to install a double pole FCU as a means of isolation for maintenance or if the unit develops a fault.

if you're installing in conduit, why not use 2.5mm singles?

But the rotary isolator will isolate the whole lot for maintenance, what extra advantage would the FCU give?

With regards to using not using singles, it's purely because I already have a few metres of T+E laying around.
 
No because the Evaporator (indoor unit) is fed directly from the condenser (outdoor unit) You isolate the entire system for maintenance. Isolating the indoor unit only could cause damage to the outdoor unit.

Yeah, I'm quite happy from an isolation point of view, knowing that turning of the rotary isolator outside would kill both units.

My main concern was whether it needed to be seperately fused as it's taken off the mains ring circuit and is feeding what is effectively a fixed piece of equipment outdoors.
 
Yeah, I'm quite happy from an isolation point of view, knowing that turning of the rotary isolator outside would kill both units.

My main concern was whether it needed to be seperately fused as it's taken off the mains ring circuit and is feeding what is effectively a fixed piece of equipment outdoors.
You said in your original post that you would spur off from the Ring Final Circuit, you never intended not to fuse that spur did you? A separate circuit would be the best idea, you may find when the A /C people come to fit the system, they will require a feed directly from the CU on a separate OCPD (fuse circuit breaker)
 
Last edited:
You said in your original post that you would spur off from the Ring Final Circuit, you never intended not to fuse that spur did you? A separate circuit would be the best idea, you may find when the A /C people come to fit the system, they will require a feed directly from the CU on a separate OCPD (fuse circuit breaker)

Well, I originally intended to fuse it, and then just wondered if it was strictly necessary as you've got an isolator for isolation purposes and the ring circuit has its own protection. The load is lower than a single 13amp socket. I just wasn't sure what 'actual' advantages it would give. (If you take away regulatory requirements)

The a/c people said they'll fit and then test on temporary supplies. I can install the permanent wiring and isolator afterwards.
 
Well, I originally intended to fuse it, and then just wondered if it was strictly necessary as you've got an isolator for isolation purposes and the ring circuit has its own protection. The load is lower than a single 13amp socket. I just wasn't sure what 'actual' advantages it would give. (If you take away regulatory requirements)

The a/c people said they'll fit and then test on temporary supplies. I can install the permanent wiring and isolator afterwards.
I have to say that's a cack handed way of doing things, will you be testing the installation, do you have the right equipment, how will yo ensure the spur you intend to install is not a spur off of a spur?
 
Well in that case don't worry about the fuse, or the conduit, or the T&E, just dangle a couple of bits of bare copper down the wall to it!

That's a fairly silly comment. Just because something is a regulatory requirement doesn't always mean it serves a useful purpose.

In this instance I'm not sure what value the in line fuse adds, hence why I questioned it.

Please feel free to explain the fault scenario where this helps so I can understand.
 
The switched fused spur connection unit is for overload and shock protection (although the existing ring main circuit should have RCD protection for additional protection).
 

Reply to Outdoor isolator installation query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
492
Just had three split Air Con units installed at my home, the ones with an indoor and outdoor unit. I (perhaps naively) trusted the installers...
Replies
2
Views
1K
D
Hello all. Split aircon with an external and internal unit both needing power. It seems the external takes the power and then there is an onward...
2
Replies
35
Views
3K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock