Discuss Oven switch isolator is missing, C2 on EICR in the Electricians Jobs area at ElectriciansForums.net

This electrician job is going for grabs, please don't post contact details in this area of the forum. Use the forum messaging system instead.
Mike ....... I think this is more appropriate ....

MP.jpg
 
This was covered earlier.
You cannot "C anything" unless it contravenes a regulation in BS7671.
There is no regulation that says that ovens must have a point of isolation. There's mention of such a thing in the OSG book (written by the Brothers Grimm) but its a guide, and there's no corresponding regulation.

So, again, if someone cares to find a relavent regulation , and prove me wrong, then go ahead.
 
Thank you all for your views, interesting discussion as with few different opinions. I will install isolator after I've spoken to a client as means of convenience and to avoid any potential issue with BCO. I do also think it's isn't a requirement. The oven is electric which I think it's irrelevant.

Thanks
 
Thank you all for your views, interesting discussion as with few different opinions. I will install isolator after I've spoken to a client as means of convenience and to avoid any potential issue with BCO. I do also think it's isn't a requirement. The oven is electric which I think it's irrelevant.

Thanks

Whats the BCO got to do with it?
 
A always note it on an EICR if there is no appliance isolators
If I want to prove a point I download the installation manual for the appliance - these almost always state an isolator with a 3mm DP contact switch is required.
As manufacturers instructions over ride the regulations then it is a warranted observation.
IIRC it says something on the onsite guide about appliance isolators in kitchens , but I cant be bothered to go to the van as it is raining outside (book in van)
 
I have not got the new regs to hand (office needs a tidy)
The previous regs had
Section 134 ERECTION AND INITIAL VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection
Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

PART 5 SELECTION AND ERECTION OF EQUIPMENT
CHAPTER 51 COMMON RULES
510.3 Every item of equipment shall shall be selected and erected so as to allow compliance with the regulations stated in this chapter and the relevant regulations in other parts of BS7671 and shall take account of manufacturers' instructions.
 

Reply to Oven switch isolator is missing, C2 on EICR in the Electricians Jobs area at ElectriciansForums.net

Similar Threads

Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock