Discuss Overhead tns in the UK Electrical Forum area at ElectriciansForums.net

Nickj

-
Reaction score
79
Hi guys,

Went to see a property today.

Just wanted to clarify the supply type with you.

I believe it's overhead tns but others have told customer it's overhead tt.

Could you share your thoughts?

There are 3 incoming cables that come from above the house and run down into the suppliers equipment.

As they are supplying the earth I believe it is overhead tns

Picture attached as a picture paints a thousand words

View attachment 35751
 
Difficult to tell from that blurred picture :)

The only way to be sure is ask the DNO, they might even change their supply cable and convert to TN-C-S?
 
Dno wouldn't comment. They said they can provide an upgrade to pme at cost to the customer.

If it's overhead tns as I suspect then I see no reason to force additional cost to customer to change to pme...

The dno definitely are supplying 3 seperate cables to the house. Whether they have them as tns or tncs is impossible for me to say really?

The fact they are providing 3 wires rules out overhead tt? There is definitely no rod at the property as the only means of earthing is throigh the dno supplied cable...

Grrr
 
It was only a brief look and I didn't take a Ze as I'd have needed a ladder.

No up front rcd, I had a Zs on sockets of 0.51.

Overall I'm airing on side of tns or tncs and ruling out overhead tt (based on them providing 3 cables).

Dno say they have no idea and we're just interested in charging to change to pme
 
Hi - agree 3 cables and looks like TNS, perhaps check Ze and if between 0.35 and 0.8 then most likely TNS ?
Edit : tooo slow typing, with 0.51 Ze it ain't TT and afaik it's too high for their own stated target for PME.
 
Dno wouldn't comment. They said they can provide an upgrade to pme at cost to the customer.

If it's overhead tns as I suspect then I see no reason to force additional cost to customer to change to pme...

The dno definitely are supplying 3 seperate cables to the house. Whether they have them as tns or tncs is impossible for me to say really?

The fact they are providing 3 wires rules out overhead tt? There is definitely no rod at the property as the only means of earthing is throigh the dno supplied cable...

Grrr
Have you done a loop test L-E & L-N this gives usually a good indication
 
i would have thought TNS to.

Have a look at the poles, some of them in my village you can see every few poles dogged down to Tera Firma. But it's probably not PME if the DNO is trying to sell you a conversion.

Edit: Wilko's got it in the bag.
 
Hi wilko,

0.51 is the rfc Zs not the Ze. Was unable to take a Ze due to lack of ladder. Will take that when there next.

As dno is supplying 3 cables and as they are trying to sell pme I'm going to go with tns.

Dno are really not as helpful as they should be!
 
The roof of the house with 3 cables. All properties on the street appear to be the same, 3 cables coming from the roof of house down the exterior wall and into the dno equipment as per the picture
 

Reply to Overhead tns in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
874
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
I found this in a property today, I've never seen the incoming cable to the head (above and the other side of this wall) just dangling in free...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock