Discuss Overload protection omission in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
3
Hi folks, not posted in a while but I have been having a few interesting discussions about this one !!!

I have come across a cooker connection outlet which is wired in 6mm and supplied via 45a dp sw and a 32a MCB

Now in this outlet I have an oven at 3kw wired in 2.5mm HOFR and a sparker for the hob wired in 1mm flex.

Guy from work reckons this is a C1 as the 2 cables are not rated to 32 amps. I disagree with him, While I think it is bad practice and would probably fit dual box with 2 s skts or spurs.

My take on it though is it could probably be coded c3 due to the fact that the oven and sparker will not draw anymore load than what they are rated at and the cables supplying them are adequate for that load hence overload protection may be omitted. As long as my circuit complies with fault protection requirements, it is not best practice and I would improve but would it warrant a C2 or C1!! And an unsatisfactory EICR ?? In my opinion no. But I have heard a few different opinions on this one !!!
 
What you describe is NOT a C1 - a C1 is danger NOW.... i.e live components that can be touched.

Could be a C2 BUT you can reduce the CSA of a cable and as long as the cable is less than 2 meters - so no code.

If I did the EICR, I would probably comment on the set up to CMA
 
Does the ignition circuit cable incorporate a cpc. Have you considered short circuit protection between line/neutral, I would personally C2 this.
 
Does the ignition circuit cable incorporate a cpc. Have you considered short circuit protection between line/neutral, I would personally C2 this.

There is a CPC in the sparker cable yeah, with regards to l/n short circuit is that going to be an issue over 2m of cable ? I am no an engineer so not sure, but is the situation any different from a 2.5mm spurred of a ring on a 32a MCB ? This could easily be more than 2m long ?
 
You need to consider the magnitude of fault current on the 1.0 cpc regardless of cable length. Conductor csa should be selected so it can withstand fault current with no adverse effects.
 
What is this 2 meter rule?
I'm aware of fault protection and overload protection being placed on the load side at a maximum Of 3 meters when there is a reduced ccc or reduction in CSA and 2 other considerations required but not sure on this 2 meters?
 
Last edited:
Would be time to do everyone's favourite adiabatic equation to see if the thermal constraints of the 1.0mm are adequate for a32amp mcb.
Or if the let through energy is Less than the formula K2S2 => I2t
Bit of a chew on really
 
Last edited:
Had a quick look in the BYB. The '3m rule' is to do with reg 433.2.2.
Something for me to read in a bit more detail and compare against fault protection requirements sometime.
 
Last edited:
Had a quick look in the BYB. The '3m rule' is to do with reg 433.2.2.
Something for me to read in a bit more detail and compare against fault protection requirements sometime.
The '3 meter rule as it were comes with 2 other stipulations so all 3 have to be met to comply not just the fact it's under 3 meters and fault/overload protection still needs to be installed after the '3 meters' protecting the load side
 
Aside from it not being provided with suitable circuit protection I find it difficult to believe it is actually correctly restrained at the outlet plate.
 
It's not only the flex you can see - how do you know what kind of wiring is inside between the input and the internal fuse? The hob manufacturers will have considered this when stipulating the required protection and I doubt the their instructions permit fusing at 32A. You only have to take the MI into account, but you would be hard pressed to justify ignoring their recommended max S/C protection.
 

Reply to Overload protection omission in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
From another thread: I'm thinking about this and it's got me all confuzzled. Don't fuses protect anything downstream ie my laptop's charger...
Replies
16
Views
2K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
798
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock