Discuss Override switch for Timer in the UK Electrical Forum area at ElectriciansForums.net

SJA79

-
Reaction score
1
Hi,

I've been asked to provide an override switch remotely for some external lighting which is on a din rail Timer so they would like to if required, to turn lights off if Timer is in operation and vice versa turn lights on if Timer is off. Would a 3 position switch like this do the trick and negate the need for a relay? 20 Amp SP 2 Way and Off Grid Switch - https://www.tlc-direct.co.uk/Products/MKK4899.html There will be 3c from the Timer to switch and 3c from switch to lights.

Thanks and any other suggestions welcome. :)
 
Providing it is an on/off/on (i.e. position 1 - common -> L1, position 2 - no connection, position 3 - common -> L2 - or equivalent), then yes you can do it.

Common - Line
L1 - Switched Line -> Switched contact COMMON on timer
L2 - Switched Line -> Switched contact NO on timer

The timer is running permanently. With switch in position 1, the light is controlled by the timer, position 2, it's off and position 3 it's on permanently as the timer is bypassed.

I was about to post saying no it's not possible with a single switch, but it is.

Edit:- Just re-read your post, you can't do it with 3 core from timer->switch and then switch->light.

3 core+e from switch->timer and then onto the light is possible, but you're a core short in the cable from the timer because you need a neutral to go on to the light.
 
Last edited:
Re-read the OP just to be sure and I missed the bit about 3c from timer to switch and then 3c from switch to light. Using the on/off/on switch with the cabling as described is not possible because you don't have enough cores in the cable from the timer to the light to include a neutral. It will work if the cabling goes 3c+e from timer to switch and then from timer to light.

If the cabling is already fixed, you need to use two switches. One 2 way and one 1 way (or two 2 ways) connected as shown below.

TimerWithOverride2.png
 
Hi Sparkychick,

Thanks for the replies.

Apologies I meant I am running in 3c&e earth and doing away with the existing 2c &e. My initial concern was even if they only wanted to override the timer to perm on (and use a normal 1g2w switch) then there would be backfeed to the switched side of the timer which could possibly cause damage to the unit so your answer has confirmed my thinking. As you say a 2g switch in series would also have been an option.

Many thanks for the help, I'll try the 3 position sw and see how it goes.

S
 
Providing the timer is a mechanical switch, and not an electronic device and the contacts are entirely separate from the timer control supply, then you should be fine.
 

Reply to Override switch for Timer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
891
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I need to handle power failure for my electric strikes in my house. Of course, I can leave the keyed entry on the knobs, but what if I wanted to...
Replies
8
Views
821
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock