Try not to do PA Testing but had to do it today!
Was doing the above today after a cottage got flooded. Lead didn't appear to be wet, but failed the insulation test @ 0.7Mohms, this was at a test voltage of 250V.
Re-tried it with my installation tester at 100V and 50V and got the same readings. I thought a surge protector should pass insulation testing if test voltage is 250V or less, or am I being dumb, or is the lead really duff?