Hi Guys

I've just had a discussion with my boss about cable sizes when pat tesing 415v equipment.

This is how i have been dealing with cable sizes.

If i have an extension lead with 32A plugs and sockets on I always make sure it has a minimum of 4mm cable so that it is capable of carrying the full load current of 32A as i have no idea of what equipment will be plugged into the extension lead.

On the other hand if i have a new piece of equipment delivered to the factory it may have 2.5mm cable, 32A plug, but the rating plate states the device only draws 10A for instance. Providing all other checks are ok I would pass this equipment. As i know that the cable is capable of carrying the load as i know what is fitted to it.

Now my boss had a welder delivered recently which had 2.5mm cable and the rating plate stated it draws 10A. He wouldn't fit a 32A plug on it as the the cable would be underrated for the supply it was being plugged into and under fault conditions the cable could draw more current than the cable was intended to carry and could catch fire. So what he did was fit a 16A plug. He then made a made a portable box with a 16A mcb fitted. This box was then fitted in between the 32 mains socket and the device.

Now I understand why he did this but as the main pat tester I'm now unsure of where my responsibilities end.

Should i pass equipment with 2.5mm cable and 32A plugs.

We dont have 16A sockets on the shop floor at the moment so fitting 16A plugs isn't an option at the moment.

Cheers
Nick
 
Nick, Do you have a copy of the CoP for ISITEE (PATesting) as it was? you should find all your answers in the CoP.
 
LOL

I'll re check but I'm not convinced I'm going to find the answer.

With single phase equipment you often have cable lower diameter cable than the 13A socket but then its covered by the fuse I guess.

Pat testing 3 phase seems a bit more of a grey area to me
 
Right I've just rechecked the cop and gone right through the contents list and I can't find any reference to my problem.

Are there any other pat testers on here who test industrial machinery that could point me in the right direction please.
 
You can consider the appliance rating in regards to cable csa. For a 32A extension lead I would however suggest the cable should be rated at 32A.
 
Ok so you basically do the same as me.

What about the plug, would you be happy to fit a 32A plug, providing the csa of the cable is large enough to carry the design current of the appliance, but not necessarily 32A.
 
My thoughts are you are doing a pat test of the portable appliance only. I have basic knowledge but I just feel that everything else is not your concern. Been on many jobs and an 32A plug is connected to an 2.5 but the mcb is 16. An 13A, 3 pin plug does not have to have a 13A fuse.
 
If i have an extension lead with 32A plugs and sockets on I always make sure it has a minimum of 4mm cable so that it is capable of carrying the full load current of 32A as i have no idea of what equipment will be plugged into the extension lead.
For flexible cables, you need to refer to Table VI.1 on page 134 of the ISITEE book. 4mm2 cable in rated to 25A, not 32A.

He then made a made a portable box with a 16A mcb fitted. This box was then fitted in between the 32 mains socket and the device.
What's on the end of the MCB - a 16a or 32a socket I presume?

Now I understand why he did this but as the main pat tester I'm now unsure of where my responsibilities end.
It looks like you have a portable distro - inspect and test it in the same way you would a Rubber Box type distro.

LOL
Pat testing 3 phase seems a bit more of a grey area to me
When testing three phase extension leads, make sure you do proper insulation tests between the cores. Those IEC60309 "PAT adaptors" with the phases commoned are OK for the earth continuity test, but not for the insulation resistance test. Any breakdown in insulation between the three lines would go undetected, unless they are tested separately.
 
When testing three phase extension leads, make sure you do proper insulation tests between the cores. Those IEC60309 "PAT adaptors" with the phases commoned are OK for the earth continuity test, but not for the insulation resistance test. Any breakdown in insulation between the three lines would go undetected, unless they are tested separately.[/QUOTE]
A PATester does not IR test between line/neutral anyway as the tester internally links these two and tests to earth only. This would be the same scenario for multi phase equipment when using an adaptor.
 

Reply to Pat testing cable size in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
639
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
664
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
549
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock