Discuss PAT testing question in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
0
Hey all
So my boss has got me PAT testing for the firm now but ive a quick question -

A few times when conducting tests on class one equipment ive noticed some slight arcing occur - does anyone else experience this and what is it as it shouldnt happen surely?

Thanks

D
 
I assume this is for the earth bond test between the croc clip and connection to the appliance. Ensure the connection is sound and you should not experience this. If your tester is a mains operated unit as opposed to a battery driven one the earth bond can put out 25A on an earth bond test, any loose connection you will experience arcing and inaccurate results.
 

Reply to PAT testing question in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix -...
Replies
14
Views
2K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
656
As (I believe) PAT testing includes fixed equipment connected to the electrical installation by an FCU (eg hand driers, built in ovens etc.) I...
Replies
17
Views
4K
Has anyone else noticed that AM2 Testing now has 10 questions at the end and that they are a lot harder than pre-Sept22 AM2
Replies
0
Views
961
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock