Discuss PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

I was also thinking of Reg 526.1 as well to why you should earth the back boxes with a lead.

I don't believe the screw achieves that ....

So your not confused, my position is;
I'm with putting the fly lead in, I think that is the right way. I am also on the opinion the back boxes is an exposed conductive part. regardless of it being buried in the wall.

But I am now starting think about it, but I have taken on board the thoughts and option of everyone on here and there information from and GN8. this is leave me with a question.
how would you code this on a EICR. C3 or not bother ?...

Anyway enough for today. Happy new year everyone we'll pick this up next year
 
Pirate peeks above parapet...
Question:

If you have a metal back box, whether with a fixed and moveable lug or not, the faceplate screws earth the cpc to the box, so the only danger is if a live comes loose and touches the back box, maybe when you are removing it for inspection, at which time it really ought to be isolated, but might not be if for testing?
Maybe a live comes loose and touches the back box due to poor installation...
I don't know, I'm only asking...
but what is the problem with just taking a cpc from the faceplate earth terminal to the back box? I mean, it's just 6" of wire, and takes less than a minute to do?
If installing surface mounted metal boxes with metal faceplates, you would take an earth from the faceplate to the box, wouldn't you?
Is there a downside I'm not seeing?
 
Yes, Spin...that is the downside, but as my post said, it takes less than a minute...
I know, 200 sockets in an industrial unit = a lot of extra time, but for most folks it's maybe 20 or 30 sockets at a minute each...
My analogy is putting on a lifevest when I go out boating...it takes a minute...
 
Why are folks getting so excited about adding the flylead if its a metal accessory?
I can kind of understand if you mean when replacing a plastic light switch for metal, and cpcs were already terminated in back box, easier just to add fly lead, but in every other instance I'd always prefer to run cpcs direct to accessory, and leave it at that.
For some reason on metalclad surface mount gear I always fit a flylead, but tend not to bother with flushboxes. Beginning to question the logic with that but there you go!
 

Reply to PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
849
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
924
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock