  1. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    My PV system (4kWp of panels with a Power One Aurora PVI-3.6-OUTD-UK inverter) seems to regularly peak at 3608-3610 W. In reading the literature on the inverter I was expecting to see a peak output of 16A which is 3680 watts at 230 volts or 3840 watts at 240 volts. Grid voltage as seen by the inverter is typically 238-242 volts when the system is in full flow. I know the inverter has 3600 in its model name but I’m curious why the output doesn’t match the literature. Any insights appreciated.
     
  2. moggy1968
    Offline

    moggy1968 Electrician's Arms

    what time of year did you achieve 3610?
     
  3. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    21 Jan and 7, 12, 16, 18 and 19 Feb - seems too much of a coincidence that it's the same peak value.
     
  4. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    Here's a graph of today's out - note the definite flattening at 3600

    solar output.jpg
     
  5. TJLinks
    Offline

    TJLinks Electrician's Arms

    Where/how do you generate a graph like that?
     
  6. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    Data extracted from the inverter via Aurora Communicator and then plotted in Excel...
     
  7. yellowvanman
    Offline

    yellowvanman Electrician's Arms

    Location:
    Dorset
    Probably something to do with the 'tolerances' of the inverter.
     
  8. screwdriver
    Offline

    screwdriver Electrician's Arms

    I take it that you are in the UK and have a nice high south facing steep pitch roof? If so how about giving it a few months until there is a bit more sun :) I have seen the PVI 3.6 OUTD UK peak at 4015w before on a 3920w system so I wouldn't worry too much!
     
  9. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    I am indeed: Hampshire, 40 deg roof, 10 degrees east of due south.

    Happy to wait a bit but the consistent peak value did make me think there was a ceiling somewhere. I've now gone back and looked at the inverter log files and the DC peak wattage from the panels appears to be roughly 3700 watts so perhaps it all makes sense for the time of year.
     
  10. screwdriver
    Offline

    screwdriver Electrician's Arms

    Out of interest, what does your inverter show up as in the communicator? a PVI 3300?
     
  11. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    Yes, it shows up as a PVI-3.3-OUTD-UK - I understand this is something to go with G83 compliance for the UK.
     
  12. Graddie
    Offline

    Graddie Guest

    Hi We have a PVI 3.6 (16amp limited) and are also peaking at 3681W. I am waiting for a response from Power One as I agree that 16A at 240V is 3840W.

    Regards
     
  13. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    What sort of grid voltages are you seeing when those output levels occur?
     
  14. GaryM
    Offline

    GaryM Guest

    Does you local grid deliver 240V or 230V? 3681W at 230V is 16A.
     
  15. Sunshine777
    Offline

    Sunshine777 Regular EF Member

    In my case when the inverter is outputting 3600 watts the grid voltage it reports is typically 240-243V. On average when the inverter is outputting more than 200 watts the voltage is over 240. At start-up and shut-down the voltage is nearer 235.
     