Discuss Peculiar results on rcd trip test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

james beckford

Afternoon everyone, got a weird one for you all.

Installed electric shower, had to upgrade consumer unit at same time, carried out all dead testing etc, Ze and Zs all good, insulation test perfect HOWEVER

when carrying out RCD trip test from the connector block terminals in the shower the RCD will not trip on I delta 1 at 0 degrees. trips perfectly at all other test settings.

went back and carried out all testing again everything else fine.

im using a fluke if that has any bearing

Thanks in advance for any useful answers.
 
Yep, have to agree. Test at the actual RCD and see what results you get there! If the results there are OK Im dumbfounded as to why they are not OK at the shower .....
 

Reply to Peculiar results on rcd trip test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
563

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock