Hi, Guys,when measuring PFC-PSCC on 3 phase supplies,I know that you test between live conductors L1-L2, L1-L3, L2-L3 and then all 3 to Neutral and note lowest reading obtained. Then all 3 phases ( is that right term for C&G? ) to earth. Then neutral to earth and lowest reading obtained recorded Are these readings times x 2? Thanks. PS hardly ever worked on 3 phase.

ops think I'm getting mixed up with testing a 3 phase cable for IR
 
Last edited:
You have described the IR testing.
For PSC you test L1-N, L2-N, L3-N take the highest reading and multiply by 2 to give the three phase PSC to record.
If, and only if, your meter can measure PSC on 400V would you be able to safely test the line to line short circuit current. This is not part of the recommended test procedure.

For PEFC you test L1-E, L2-E and L3-E and record the highest value.

The highest of the two recorded values (which will be the three phase value) is the PFC.
 
Once again, thanks Richard. Yes i realised I was getting mixed up. If doing a 3 phase Ze test lets say in a factory, what procedure would take place whist earthing conductor removed to test? Would the whole factory have to be shutdown?
 
Once again, thanks Richard. Yes i realised I was getting mixed up. If doing a 3 phase Ze test lets say in a factory, what procedure would take place whist earthing conductor removed to test? Would the whole factory have to be shutdown?

You can't leave a system engerzied with the earth disconnected, so yes it has to be switched off/isolated. Arrange a time which is best for the client.

How ever most of the time in real life this isn't possible, a factory isn't going to shut down while you take a Ze measurement. So you take it with everything still connected and record it on your certificate and the reasons why.
 

Reply to Pfc - pscc on 3 phase supplies in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
508
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
636
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock