Discuss PIR coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

mainebankelec

Just finished a periodic in a domestic premises due to be up for rental shortly.

My query is,

Supply is TNS

Counsumer unit is metalclad with tails entering bottow of DB through bushed holes but the tails are not rcd protected?

Should this be code 4 as does not complie with current edition

Many thanks
 
Sorry confused myself reading and typing lol

First issue : Supply tails from meter enter a metalclad consumer unit do these require coding

2nd issue: At present there is no main bond to oil line code 2 but to be able to bond the oil line the bonding conductor is going to have to be outside at the oil tank as there is no copper oil line inside the property just the flexible pipe you see at the burner.?
 
Just finished a periodic in a domestic premises due to be up for rental shortly.

My query is,

Supply is TNS

Counsumer unit is metalclad with tails entering bottow of DB through bushed holes but the tails are not rcd protected?

Should this be code 4 as does not complie with current edition

Many thanks
I don't see a compliance issue with this on a TN-S supply, as long as the cable entry holes are bushed or grommeted, therefore NO coding required. If the supply was TT and a metal-clad board, then the tails would require RCD protection, then potential danger exists, Code 2.
 
Last edited by a moderator:
Re the tails, if the meter and the CU are in the same area I wouldn't code the "issue" at all - but that's only my opinion.

Re the oil line - if its flexible, do you mean not metal?
 
Last issue is the main incoming supply to building has bonding clamps fitted to the main supply cable in two places with both clamps interconnected and then one piece of 16mm earth to the esco. Would you just note this on certificate and ask the customer to check with supply authority if this is adequate?
 
It is still metal. The main oil comes from the oil tank about 1m in normal copper piping then as it enters the property it changes to the flexible metal coated pipe. If i stuck a clamp round this it would just compress and not provide an adequate bond. But i read somewere previously that you could not bond pipe to the external of a premises?
 
If you think that the oil line will introduce a potential into the property, bond the rigid (not flexible) oil line at the nearest point of entry to the property (inside or outside) NOT at the oil tank.
 
Last edited by a moderator:
I don't see a compliance issue with this on a TN-S supply, as long as the cable entry holes are bushed or grommeted, therefore NO coding required. If the supply was TT and a metal-clad board, then the tails would require RCD protection, then potential danger exists, Code 2.

Code 2 a TT with no RCD on tails? So would you insist on it being a 100mA RCD? For tails outgoing circuits


---
I am here: http://maps.google.com/maps?ll=52.589702,-1.100750
 

Reply to PIR coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Good Afternoon All, I have just completed a Periodic test on a house and have a question about the meter tails. The house is 14 years old so has...
Replies
11
Views
5K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K
I often work alongside a small team of other trades on flats and house refurbishments for private owners, however on a slightly bigger project...
Replies
14
Views
3K
Just trying to understand if a 15yr old first floor flat, should be refused certificate because no RCD present. Has PIR code4 been scrapped? Is...
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock