asbarker

Hi, I have recently carried out a PIR on a church. The equipotential bonding to the gas and water go back to the sub main in a meeting room where the stop tap and meter are. What code should be assigned as these should go back to the origin?
 
Re: PIR codes

Hi, I have recently carried out a PIR on a church. The equipotential bonding to the gas and water go back to the sub main in a meeting room where the stop tap and meter are. What code should be assigned as these should go back to the origin?

Not neccessarily.

You now need to do the calcs to ascertain wether or not the earthing conductor of the distribution circuit is large enough to do the job of CPC and MPBC.

If it is, the water & gas bonding conductors are connected to what is technically known as a BEMT (Building Earth Marshalling Terminal). There is nothing wrong with this arrangement providing the earthing conductor above is large enough to function as both above.
 

Reply to PIR on a Church. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
926
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock