I have fitted an independent PIR in the hall way.
When energising PIR, the light comes on and stays on.
When the sensor is activated, the light goes out???
I have wired it as to the suppliers diagram.
Is it a faulty PIR????

mick223
 
Hi Mick - Welcome to the forum ...

If your in active training and on a course or just about to start one you can go to our section 'Apply for access to the Training forum' and follow the instructions - we have selected Mentors to guide you and its suited ideally for the level of questioning we find from our trainee's.

In answer to the question - does your PIR have normally open N/O and normally closed N/C options if so you may find moving the wire from the N/C output to the N/O may cure your problem.

Can you give us a make and model of the PIR?
 
The sensor in a PIR or motion detector is actually split in two. The reason for that is it is looking to detect motion change and not average IR levels. The two halves are wired up so that they cancel each other out. If one half sees more or less IR radiation than the other, the output will swing high or low depending on the type of PIR. If your sensor is normally closed switch then when the sensor is triggered it will open the circuit cutting the supply of power to the load and vice versa. Check the sensors specification and or setting.
 
The sensor in a PIR or motion detector is actually split in two. The reason for that is it is looking to detect motion change and not average IR levels. The two halves are wired up so that they cancel each other out. If one half sees more or less IR radiation than the other, the output will swing high or low depending on the type of PIR. If your sensor is normally closed switch then when the sensor is triggered it will open the circuit cutting the supply of power to the load and vice versa. Check the sensors specification and or setting.


Welcome to the forum yarasa ... the OP has resolved the issue as stated in post 3 and we have heard nothing back since, appreciate your input either way and hope to see your contributions and/or any questions you may have :)
 

Reply to PIR sensor problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
435
I'm trying to wire in a 4 core capacitive sensor into a safety circuit. I have brown, blue, white and black coloured cores and it's a NO sensor...
Replies
1
Views
210
I have replaced a staircase timer because the previous one was fault. There was a problem the light stayed on all the time. When i replaced the...
Replies
3
Views
825
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
517
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock