is it

a. the test ensures all fuses, signle pole switches and themo are connected in L only. although this doesnt apply to the swa. but it checks all three lines are correcftly identifiied throught the system

b. for safety reasons.
 
Pretty much......but add to b. that you wouldnt want to energise an installation with incorrect polarity.....and regarding a. you are checking the polarity of the SWA according to the question,not the entire system.
 

Correct sequence for safe domestic electrical testing


BEFORE CONNECTION OF THE SUPPLY

1
Continuity of protective conductors

2
Main and supplementary bonding continuity

3
Continuity of ring final circuit conductors

4
Insulation resistance

5
Site applied insulation

6
Protection by separation

7
Protection by barriers and enclosures

8
Insulation of non-conducting floors and walls

9
Polarity

10
Earth electrode resistance if an earth electrode resistance tester is used

WITH THE SUPPLY CONNECTED

11
Earth electrode resistance if an earth-fault loop tester or the ammeter and voltmeter method are used

12
Confirm correct polarity

13
Earth-fault loop impedance/PFC/PSSC*

14
Correct operation of residual current devices

15
Correct operation of switches and isolators
 
Last edited by a moderator:
to put it simply, if you test it dead and the readings are good, there's less chance of it going bang when you switch on.
 
Visually check all connections so you know all connections are in the correct terminals, and all connection are Identified.3 core swa correctly identifed (Brown Black Grey - Brown Blue Green/Yellow).
 
Umm, what about prospective fault current, seems to be missing from the above list (to be verified before switching any circuits on)?
 
Umm, what about prospective fault current, seems to be missing from the above list (to be verified before switching any circuits on)?

My instruments display both so I guess it's classed as one...anyone?

But added, will be emailing the company to add it to their web site !! No Hope..
 
Umm, what about prospective fault current, seems to be missing from the above list (to be verified before switching any circuits on)?

Step 13 both PEFC/PSSC, to ensure that all your protective devices are suitably rated before energising.

Edit: PFC->PEFC.
 
Last edited:

Correct sequence for safe domestic electrical testing


BEFORE CONNECTION OF THE SUPPLY

1
Continuity of protective conductors

2
Main and supplementary bonding continuity

3
Continuity of ring final circuit conductors

4
Insulation resistance

5
Site applied insulation

6
Protection by separation

7
Protection by barriers and enclosures

8
Insulation of non-conducting floors and walls

9
Polarity

10
Earth electrode resistance if an earth electrode resistance tester is used

WITH THE SUPPLY CONNECTED

11
Earth electrode resistance if an earth-fault loop tester or the ammeter and voltmeter method are used

12
Confirm correct polarity

13
Earth-fault loop impedance/PFC/PSSC*

14
Correct operation of residual current devices

15
Correct operation of switches and isolators

Have never liked the phrase "with the supply connected", alot of people get this confused with turning on the main switch, whereas steps 11,12 and 13 should all be carried out with installation isolated
 
Have never liked the phrase "with the supply connected", alot of people get this confused with turning on the main switch, whereas steps 11,12 and 13 should all be carried out with installation isolated
You mean circuit isolated surely, ergo mcb in CU, but then try doing a polarity check/eli/pfc/pssc with the power not energised?

Reading too deep into this its the methods to get the correct polarity, on 1 garage supply...not a full installation...
 
My understanding of the term PFC (prospective fault current) is that it is the higher of the PEFC and PSCC, so you normally just list "PFC" which is taken to mean you measure both PEFC and PSCC and record the highest. Alternatively you could list out "PEFC" and "PSCC" and still just record the highest. (For a single phase system, at least).
 
You mean circuit isolated surely, ergo mcb in CU, but then try doing a polarity check/eli/pfc/pssc with the power not energised?

Reading too deep into this its the methods to get the correct polarity, on 1 garage supply...not a full installation...
No, he does mean installation isolated, at this point. The supply should be connected to the CU, but the main CU switch should be in the off position.
 
You mean circuit isolated surely, ergo mcb in CU, but then try doing a polarity check/eli/pfc/pssc with the power not energised?

Reading too deep into this its the methods to get the correct polarity, on 1 garage supply...not a full installation...

Before adding a circuit you should carry out a test on earth fault loop impedance (Ze), for which you should be disconnecting the earthing conductor so installation needs to be isolated
 

Reply to polarity testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, I've recently done a PAT course after the large company I work at discovered we have a Deltapat 3309 kit tucked away. I'm actually an...
Replies
1
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
850
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
845

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock