currently working through a EICR on a empty care home soon to be refurbished and new clients to move in.
Distribution circuit from DB 1 feeding DB3( supplying sockets/ lighting etc) fed from a C type bs en 60898 mcb 63 amp.
Max zs 0.34(100% value)
Measured zs 0.34 ( over the 80% correction factor at site measured temperature)
DB 6 fed ( supplying sockets and lighting)from DB 3 on a 40 amp type C bs en 60898.
So a sub main feeding a DB feeding another submain for another DB all 3 phase.
A discrimination/ design nightmare all carried out in 2006, no EIC , electrical/mechanical or design drawings.
And they say domestic is bad!!
No questions to ask the forum, just a rant really.