spud1

-
Arms
Reaction score
55
Hi,

I have a metal container / cabin with plastic consumer unit c/w RCD main switch and earth electrode, cabin is being supplied by a diesel generator with a bonded neutral located about 10 metres away in its own shed. Customer has tried wiring this up on their own and called me for help when they couldn’t get a voltage reading between live from the genny and the earth from the electrode . Explained that this was due to the ground earth not being referenced to the genny and that the neutral from the genny should probably also be used to Earth the cabin. But here is my question; Is it acceptable to link the neutral and earth bar within the consumer unit or should both the sub main cpc and neutral be commonly connected at the genny end?
Also in addition should there be electrodes driven in and connected at the cabin and/or genny to reference to ground earth too?

Cheers
 
Check and see if the output of the generator has a voltage to earth. Make sure before you do anything there is 30mA RCD main switch on the consumer unit. If there is no voltage to earth put a link in between neutral and earth at the incomming side of the RCD. This will reference one pole of the generator to earth so you now have a neutral and earth. Do an earth loop test and an RCD test before putting the installation in to service. An earth spike is also recommended.
 
Generators usually have a neutral-earth link inside making them TN-S.
An earth electrode is needed generally for generators above 10kva to reference the neutral to earth by connecting the generator chassis to the electrode at the generator end.
The upstream installation is then a TN-S earthing system
Guidance can be found in the on site guide and GN8
Might be worth contacting the generator company as well to confirm any earthing arrangement and recommended resistance of the earth electrode.
To measure the electrode an earth electrode tester will be needed as an earth fault loop impedance tester would be useless as the electrode doesn’t form part of the earth fault loop impedance path in this instance
 
An earth electrode is needed generally for generators above 10kva to reference the neutral to earth by connecting the generator chassis to the electrode at the generator end
Would it be advisable to install electrode at the cabin too? Or is genny electrode alone sufficient?
 

Reply to Portacabin/generator earthing in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock