Done a fuse board change on a propery, hasnt been touch since early 60s at a guess.
There is 2 ring mains, which i had split over the the 2 rcds. Each time i swithched on one, the other RCD tripped out, and vise versa.
Have no end to end on one ring main, and end to end on Line & Earth but not the neutral on the other ring.
To get it going for the weekend i put both rings on one RCD, but still tripped out.
Does this sound like a borrowed neutral problem, or a inter crossed ring main?
There is 2 ring mains, which i had split over the the 2 rcds. Each time i swithched on one, the other RCD tripped out, and vise versa.
Have no end to end on one ring main, and end to end on Line & Earth but not the neutral on the other ring.
To get it going for the weekend i put both rings on one RCD, but still tripped out.
Does this sound like a borrowed neutral problem, or a inter crossed ring main?