TJC1

-
Reaction score
6
Done a fuse board change on a propery, hasnt been touch since early 60s at a guess.

There is 2 ring mains, which i had split over the the 2 rcds. Each time i swithched on one, the other RCD tripped out, and vise versa.

Have no end to end on one ring main, and end to end on Line & Earth but not the neutral on the other ring.

To get it going for the weekend i put both rings on one RCD, but still tripped out.

Does this sound like a borrowed neutral problem, or a inter crossed ring main?
 
Yep usually is. Crossed neutrals not necessarily the rings but another circuit neutral. I hate it when that happens especially with singles circuits.
 
Done a fuse board change on a propery, hasnt been touch since early 60s at a guess.

There is 2 ring mains, which i had split over the the 2 rcds. Each time i swithched on one, the other RCD tripped out, and vise versa.

Have no end to end on one ring main, and end to end on Line & Earth but not the neutral on the other ring.

To get it going for the weekend i put both rings on one RCD, but still tripped out.

Does this sound like a borrowed neutral problem, or a inter crossed ring main?

So then only one ring, which is faulty, which you energised anyway ?
 
Hello, Yes this would indicate a cross-connection between the 2 RCDs

If it only trips when you turn the MCB on, it indicates the line conductor that has been cross-linked.
If it trips instantly when you turn the RCD on, this would indicate a cross linked neutral.

A popular cause of this is lighting circuits, someone decides they want a new light and borrow a neutral from the nearest place and a live from some other circuit.

I presume you have Tested the insulation on both ring circuits and they checked out okay, if this is the case then my advice would be to remove all neutrals and earths from the board.

While the circuits are dead, IR test between all the cables, to ensure there is no connection between any cables there shouldn't be.

If there is, use the half split method to test and locate the connection.

Doing this should locate the fault efficiently so it can be rectified.

Hope this helps.
 
Obviously not... Just after some advice.
Well, I have to be very careful here, as I can come over as a bit of a negative old git. However, it does say in your profile that you are an "electrical contractor". So, my advice would be, next time, do what you are supposed to do, as an "electrical contractor", and don't get your self into this mess, as you obviously have no idea what the problem might be. Are you going to give your customer a decent discount for not doing a particularly good job, so far? Why didn't you do any testing? What testing are you going to now do, given the problem?? I would guess that you have probably made a very basic error when you put everything back together, which will now be a bit more tricky to resolve.Oh, and BTW, what is an "inter crossed ring main", when it is at home??
 
Last edited:
Well, I have to be very careful here, as I can come over as a bit of a negative old git. However, it does say in your profile that you are an "electrical contractor". So, my advice would be, next time, do what you are supposed to do, as an "electrical contractor", and don't get your self into this mess, as you obviously have no idea what the problem might be. Are you going to give your customer a decent discount for not doing a particularly good job, so far? Why didn't you do any testing? What testing are you going to now do, given the problem?? I would guess that you have probably made a very basic error when you put everything back together, which will now be a bit more tricky to resolve.Oh, and BTW, what is an "inter crossed ring main", when it is at home??
Think he is saying, maybe interconnection between both circuits.?
 
Test first, some never learn. How can you replace a CU when you have no idea of circuit configuration, never assume because you see a pair on a device it is a ring final.
 
Yes some testing in order, IR on both circuits, but he needs to find both breaks on N if it is on a 32amp circuit, and get end to end on all conductors. L N E
 
Well well well we're feeling the Christmas spirit in here today. Surely given the OPs responses the only reply he should be getting is 'come back when you have a set of test results'?
Well HT, forgive me if I am misconstruing your comment about Xmas spirit, but it looks to me like this guy is masquerading as a competent person, charging his customer likewise, when really he is a bit clueless? Like Murdoch has said, how is the poor old customer doing out of all this? Just saying...
 

Reply to Possible borrowed neutral ring mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock