Posting a message to the forum will remove the above advertisement
  1. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

Discuss Potential difference between Earth and Neutral in the DIY Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Has anyone ever encountered a fault with a RCD which causes a potential on earth in respect to neutral?



    I am a trainee electrician, working with an experienced electrician. We encountered a fault today, earth had a potential of 238V in respect to Neutral and a 0 V potential in respect to line.



    We did an insulation resistance test at 500V on all circuits from line to neutral, line to earth and neutral to earth. All circuits gave a resistance of >999M ohm. So there is no way line and earth can be crossed anywhere.



    The fault didn't trip the RCD or the MCB, yet there was a potential difference between neutral and earth.



    We got really strange voltage readings while probing around, differences between earth and neutral ranging from 100v to over 300v, how can this be as nominal voltage was 238V.



    The potential difference between neutral and earth was greater when the RCD was in the closed position.



    All I can possibly think of is the somehow the line windings around the iron core in the RCD have made contact with the Neutral windings. Could a fault like this possibly create a voltage on Neutral, and cos it is a TN-C-S system, Neutral is connected to earth at the incoming supply, so is it possible this voltage could be seen on the earth bar in the consumer unit?
     
  2. Barry White
    Offline

    Barry White Guest

    Line and neutral reversed ?
     
    • Like Like x 1
  3. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    Hi dude,no guess would be possible,without knowing where you were measuring this voltage,and what position all the various switches/breakers,etc were in.

    Start from a position upstream,where all measurements are as expected,or if not,somebody has a bigger problem :)
     
  4. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    I just would like to know if anyone thinks it is remotely possible a fault inside the RCD could cause this issue?
     
  5. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    You've posted this on another forum.

    Why didn't you test Ze?
     
  6. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    I don't think it's even remotely possible.
     
    • Like Like x 2
  7. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Yes I got a temp ban on this forum, so I joined another one. You use two forums too, else how would you know?

    We didnt suspect the issue to be with the distributor.
     
  8. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Line and Neutral reversed coming into the distribution board?

    That could make allot of sense. We didn't do a live polarity test thinking about it.
     
  9. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    Business Name:
    David Haddock Electronic Repairs
    it's more than likely a ghost voltage !
     
  10. Rob
    Offline

    Rob Trusted Advisor

    Location:
    North west
    Sounds like a floating neutral to me.

    With the earth connected to the DNO's incoming earth, what resistance are you getting between N > E
     
    • Like Like x 1
  11. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    I'm gob smacked that 2 sparks and 1 trainee didn't check the incoming supply...... all sounds a bit smelly IMHO
     
    • Like Like x 2
  12. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    > 999 on 500v
     
  13. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    >999 on 500V
     
  14. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    So Gigsy..... are you going to update this forum with your findings reported on the other forum?
     
    • Like Like x 1
  15. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Is that necessary? I don't think anyone would be interested? Is it frowned upon to use two forums? If so why do you use more than on forum? Which forum do you like the best? Why are you making an issue with me using two forums?
     
Loading...
Similar Threads - Potential difference between Forum Date
Equipotential Bonding Electrical Forum Feb 9, 2018
Equipotential Bonding Explanation DIY Electrical Forum Feb 8, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job