    Has anyone ever encountered a fault with a RCD which causes a potential on earth in respect to neutral?



    I am a trainee electrician, working with an experienced electrician. We encountered a fault today, earth had a potential of 238V in respect to Neutral and a 0 V potential in respect to line.



    We did an insulation resistance test at 500V on all circuits from line to neutral, line to earth and neutral to earth. All circuits gave a resistance of >999M ohm. So there is no way line and earth can be crossed anywhere.



    The fault didn't trip the RCD or the MCB, yet there was a potential difference between neutral and earth.



    We got really strange voltage readings while probing around, differences between earth and neutral ranging from 100v to over 300v, how can this be as nominal voltage was 238V.



    The potential difference between neutral and earth was greater when the RCD was in the closed position.



    All I can possibly think of is the somehow the line windings around the iron core in the RCD have made contact with the Neutral windings. Could a fault like this possibly create a voltage on Neutral, and cos it is a TN-C-S system, Neutral is connected to earth at the incoming supply, so is it possible this voltage could be seen on the earth bar in the consumer unit?
     
  2. Barry White
    Online

    Barry White Guest

    Line and neutral reversed ?
     
    • Like Like x 1
  3. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    Hi dude,no guess would be possible,without knowing where you were measuring this voltage,and what position all the various switches/breakers,etc were in.

    Start from a position upstream,where all measurements are as expected,or if not,somebody has a bigger problem :)
     
  4. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    I just would like to know if anyone thinks it is remotely possible a fault inside the RCD could cause this issue?
     
  5. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    You've posted this on another forum.

    Why didn't you test Ze?
     
  6. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    I don't think it's even remotely possible.
     
    • Like Like x 2
  7. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Yes I got a temp ban on this forum, so I joined another one. You use two forums too, else how would you know?

    We didnt suspect the issue to be with the distributor.
     
  8. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Line and Neutral reversed coming into the distribution board?

    That could make allot of sense. We didn't do a live polarity test thinking about it.
     
  9. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    Business Name:
    David Haddock Electronic Repairs
    it's more than likely a ghost voltage !
     
  10. Rob
    Offline

    Rob Trusted Advisor

    Location:
    North west
    Sounds like a floating neutral to me.

    With the earth connected to the DNO's incoming earth, what resistance are you getting between N > E
     
    • Like Like x 1
  11. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    I'm gob smacked that 2 sparks and 1 trainee didn't check the incoming supply...... all sounds a bit smelly IMHO
     
    • Like Like x 2
  12. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    > 999 on 500v
     
  13. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    >999 on 500V
     
  14. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    So Gigsy..... are you going to update this forum with your findings reported on the other forum?
     
    • Like Like x 1
  15. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Is that necessary? I don't think anyone would be interested? Is it frowned upon to use two forums? If so why do you use more than on forum? Which forum do you like the best? Why are you making an issue with me using two forums?
     
  16. Gigsy
    Offline

    Gigsy Regular EF Member

    Location:
    Birmingham
    Are you now my troll?
     
  17. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    People are free to use as many forums as they wish, All I would say is it's a bit like the first rule of the Fight Club.
    Everybody knows the first rule of the fight club Right!!!!
     
  18. stantheman
    Offline

    stantheman Regular EF Member

    .......No scratching or biting??
     
  19. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    I think you're a bit of a pillock truth be told. No wonder you've already served a ban here, every post you've made has an air of arrogance about it. Go use the other forum, you serve no purpose here other than to annoy and irritate.
     
  20. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
     
    • Like Like x 1
  21. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    You could at least pop back and thank mykey for suggesting the answer to your problem. See post #2.
     
    • Like Like x 1
  22. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Isn't this the chasing across ceilings fellow again, I thought he was off in the cooler for a while, is he back.
     
  23. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    Yeah mate he served his time so play nice:D
     
  24. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    All welcome to me.
     
    • Like Like x 1