kshah86

Hello, recently qualified electrician. I’m doing a job for someone. They have a radial circuit which they want to convert to a ring. I need to run a wire from the last socket which is on the third floor back to the consumer unit. They person wants it done in conduit or trunking. I was wondering what price quote i should roughly give him. Any ideas anyone? Thanks in advance. It’s a semi detached property. 3 floors. also does this require new cert as im changing the circuit from radial to ring or can i issue a minor works cert?
 
I'm assuming that you will be changing the 16 amp MCB to 32 amps, so as such you will need a full EIC. Additionally, this is notifiable. Don't they teach you anything on these 18 day courses?
 
Last edited:
soon we'll have to notify some bureaucratic jobsworth organisation every time we wipe our arses.
 
Why on earth would a customer even ask for this alteration.

Also running back to the CU over what I presume is a fair distance won't be any good for the load balancing on your new circuit either
 
I'm with guitarist on this one, if your changing it into a ring main your pretty much changing all the characteristics of the circuit, you can now do test that couldn't have been done before, end to end etc, plus your taking the old mcb out and replacing a new one, if I replace an mcb I do NIC cert on that circuit, when you change a D.B You have to test every effected circuit on a NIC right?
 
I'm with guitarist on this one, if your changing it into a ring main your pretty much changing all the characteristics of the circuit, you can now do test that couldn't have been done before, end to end etc, plus your taking the old mcb out and replacing a new one, if I replace an mcb I do NIC cert on that circuit, when you change a D.B You have to test every effected circuit on a NIC right?

That's my point really. You are not simply modifying something which is existing, the way you might extend a radial or spur off a lighting point; you are creating a whole new circuit in name, characteristics, OCPD size and type of testing required. It is, to all intent and purpose, a completely different circuit.
Just my opinion anyway, not that it matters as the OP hasn't been back since posting. :)
 
Thanks everyone for the replies. Went to have a look at the house today. Basically the guys having building work done, but before the building work, he was getting complaints from the tenants that every so often, the rcd kept tripping. He asked the builder to have a look and the builder told him that it is because the circuit was setup as a radial and needed to be changed. When i went and had a look. Turns out the builder was wrong and he’s only good for laying the bricks. The circuit in question was already a ring. Done my tests and found the fault. One of the neutrals was not terminated in the spur socket of the ring. Once fault had been rectified I done rcd tests and everything was fine. No need for altering the circuit at all.
 
Unrelated to this but at the same house, the guy had a big living room. He has partitioned this and made it smaller to extend the kitchen. There are sockets now in the kitchen which are on the same ring as the living room which he does not want live any more as the new bigger kitchen has had new wiring and circuit installed. Is it ok to isolate the unwanted sockets in the kitchen via terminal blocks, wrap with insulation tape and cover with blank plates or not?
 

Reply to price quote for job in the Business Related area at ElectriciansForums.net

Similar Threads

So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
558
Hi all, Just wondering what the general situation is with other people on smaller jobs, do you give a quote or estimate to the client before you...
Replies
6
Views
976
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi guys. It would be really useful to run this past you and get a consensus/input from you for what would be a realistic amount to charge for an...
Replies
15
Views
1K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock