I’ve probably broken every rule in the book with this. Was asked if I could do a cable joint between a 6mm T+E and a 2c 6mm SWA. It had to be as unobtrusive as possible as I was on a front wall of a graded building. The T+E ran for 6” below the rendering corbel so the joint would be on the stonework below.
Made the joint by soldering the cores using copper ferules in side a 25mm conduit coupling. The T+E earth was again soldered to 2.5mm singles and made off to the gland on the out side of the joint. Used bent 25mm earth tags to make the brackets to hold the joint to the wall. The joint was then filled with epoxy resin. The whole joint is only 1.5” long and almost unnoticeable after I’d stone painted the whole lot.
Tests were Ph – N <.75G @ 2500V 15 seconds, Ph + N - E .5G @ 1000V 15 seconds excessive testing I know but I wanted to see if it could stand it.
 

Reply to Probably broken every rule in the book in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I
Inspected a house today and why its not a pile of ashes is amystery to me. The CU had been changed about 6 weeks ago by a spark and theclient was...
Replies
21
Views
2K
Jabbajaws
J
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
Replies
0
Views
3K
mbga9pgf
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock