I have a ----y problem as follows:

I have a ABB disconnect switch Fused at 60A, supplying 3 phase 575V(North America) to a Power Cabinet.

The Power Cabinet has several motors and a 6000VA transformer, that steps down the voltage to 230VAC/120VAC single phase.

The Cabinet also powers another Cabinet, a 15A Control Cabinet at 120VAC

Twice now, the fuses on the Power Cabinet have blown on the primary side of the transformer, and 2 VFD's
when the ABB disconnect is either being closed or opened.(We turn the disconnect off at night, and turn it on in the morning. It has only happened 2x but we have closed the disconnect probably 30-40X already.

The Transformer is fused as 6000/575V = 12A Time Delay

The 2 Motor VFD's are both 2A, and are Fused at 3.5A

What could be causing the Fuses to blow? is the transformer surging the 3 phase line?

The whole 3phase line seems to be surging, since the transformer, and the 2 motor VFD's are
the only device drawing current in the Cabinet.

Any suggestions to debug this issue?
Collin
 
There is always a huge surge when a transformer magnetises on being energised....usually 6x plus the normal full load current. You could try a type D mcb on the primary side.
 
As mentioned above transformers have a high inrush current and you may need to consult fuse manufacturers for correct type needed, but also consider the switchfuse itself if its old and the make and breaks is sluggish this will spike your suppy or if their is delay between the different phases making and breaking when you switch it on or off, the difference may only be a fraction of a second in some cases to cause problems.
 

Reply to Problem with Power Cabinet blowing fuses in the Australia area at ElectriciansForums.net

Similar Threads

I am a maintenance man but I do hold a journeyman's license I'll do my best to explain what is going on. I have 2 ea 50 Hp air compressor. one is...
Replies
23
Views
2K
Hi all, Been a few years since i've posted but here goes! At the factory I work in we have an old Spanish line from the mid-eighties that is fed...
Replies
6
Views
5K
J
I currently have a problem with a 72 kw storage heater which is blowing 100 amp BS88 about one every 4 days, it is now on its third. The fuse is...
Replies
27
Views
4K
Engineer54
E
Hi, i went to a call out a couple of weeks ago to a kabab shop. Its single phase supply. i went there and they had blown the main fuse 80amp. Iv...
Replies
5
Views
1K
SimpleSimon
S
got asked to look at a job for a friend of a friend today i know i should of done an ir test but workmate had van so had no testing equipment...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock