Discuss problems with Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

DDnot

Hi!

I was measuring Zs on a lighting circuit some time ago. First I did R1+R2 and it was around 1.60, pretty high but there were a few connections on the way and most of the cable was 1.0mm. Ze measured at the CU was low about 0.10 only, so Zs altogether around 1.70. When I measured it using Zs option on my tester Zs was only about 0.60. I know that there usually is a little difference but it should not big that big. Can you help me and tell me where possibly I was making a mistake? Thanks in advance.
 
parallel paths???? also, MFTs are not renowned for accuracy on no-trip testing.
 

Reply to problems with Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
993
OLDBOY
O
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
822
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
598
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock