Hi

Can someone explain the reason for testing the PFC and what it confirms?

And what is the reson the value is doubled for 3-phase?

Thanks
 
Last edited by a moderator:
Prospective fault current, meaning the maximum current that will flow through the system in the event of a fault


Prospective Earth Fault Current - is the L/E reading with the protective bonding in place.

Prospective Short Circuit Current - is the L/N reading.

PFC is the higher of PEFC and PSCC (almost always the PSCC figure).


 
Last edited by a moderator:
The current which is likely to flow in a circuit if line and neutral cables are short circuited is called the prospective short circuit current (PSC). It is the largest current which can flow in the system. and protective devices must be capable of breaking it safely. The breaking capacity of a fuse or of a circuit breaker is one of the factors which need to be considered in its selection. Consumer units to BS EN 60439-4 and BS 88 (HBC) fuses are capable of breaking any probable prospective short-circuit current, but before using other equipment the installer must make sure that their breaking capacity exceeds the PSC at the point at which they are to he installed.
The effective breaking capacity of overcurrent devices varies widely with their construction. Semi-enclosed fuses are capable of breaking currents of 1 kA to 4 kA depending on their type. whilst cartridge fuses to BS 1361 will safely break at 16.5 kA for type 1 or 33 kA for type II. BS 88 fuses are capable of breaking any possible short-circuit current. Miniature circuit breakers to BS EN60898 have their rated breaking capacity marked on their cases in amperes (not kA) although above 10000 A the MCB may be damaged and lower breaking currents (75% for 10000 A and 50% above that level) must be used for design purposes.
 
Hi

Can someone explain the reason for testing the PFC and what it confirms?

PFC is measured to confirm that the fault current that could occur does not exceed the breaking capacity of the overcurrent protective device i.e the main cut-out fuse.

And what is the reson the value is doubled for 3-phase?

The reason it is doubled for 3-phase is because the fault current between phases will be higher than between a single phase and neutral. It's actually 1.73 times higher but it is doubled to err on the side of caution.
 
To ensure that your mcbs/rcds can withstand the pfc. If not then they may melt and fuse closed circuit, unable to trip. Typical single phase rating is 6kA. Typical 3ph is 10kA. 3ph potential is higher than 1ph.

Sent from my HTC Sensation using Tapatalk
 

Reply to Prospecctive Fault Current purpose.... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
an overload current is classified as an overcurrent occuring in a circuit which is electrically sound has a fault between phase conductors has...
Replies
5
Views
1K
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Replies
12
Views
1K
A youtube video on 100 car batteries in parrell and what happens when various items are short circuit current tested...
Replies
3
Views
979
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock