Hi I don't know if anyone can help but I was wondering if anyone has come up with any solutions to this problem. In that we have a 210kw pv system connected to the mains panel at a big office block and they have a back up generator with auto change over fitted so when the grid fails the Generator cuts in. Obviously we then have the problem that the inverter (X 9of) will switch off when grid is lost but would then switch back on when generator is running but if this happens at the weekend for instance or when there is not much load on then the inverters would try to feed into the generator causing god knows what problems. By the way the PV connection point is about 150 mtr from the generator change over panel. Any help much appreciated.
 
Is there an external G59 relay fitted? If yes, could you wire an interlock signal from the genny (or CO switch) into the relay's contactor coil feed circuit? That's a common way of doing it

Thanks for your help. Unfortunately we didn't need to fit one on this site the DNO are getting more relaxed about them.(sods law really as normally we do build and fit them). I think it will have to be a contactor with the coil being fed from the generator feed so that when it kicks in it knocks the contactor out and there by killing the PV system?
 
Thanks for your help. Unfortunately we didn't need to fit one on this site the DNO are getting more relaxed about them.(sods law really as normally we do build and fit them). I think it will have to be a contactor with the coil being fed from the generator feed so that when it kicks in it knocks the contactor out and there by killing the PV system?

Or an mccb with auxiliary contacts for shunt trip.
 
Thanks. I am not familiar with shunt trips could you explain how they work or what they do? Thanks again

A shunt trip device can be an optional accessory in a mccb that mechanically trips the mccb when power is applied to the shunt trip terminals. The power for the shunt trip does not come from within the mccb, so it must be supplied from an external source (in this case maybe one of the neons on the change over switch)Some MCCBs allow field installlation of a shunt trip kit, however others require factory installation when it's ordered. Check the specific type for available shunt trip voltage ratings and for the method of installation.

http://www.protekuk.co.uk/mccb-data-sheet.pdf
 
A shunt trip device can be an optional accessory in a mccb that mechanically trips the mccb when power is applied to the shunt trip terminals. The power for the shunt trip does not come from within the mccb, so it must be supplied from an external source (in this case maybe one of the neons on the change over switch)Some MCCBs allow field installlation of a shunt trip kit, however others require factory installation when it's ordered. Check the specific type for available shunt trip voltage ratings and for the method of installation.

http://www.protekuk.co.uk/mccb-data-sheet.pdf

Wow thanks that sounds interesting. I will see what is available for our MCCB main switch. Thanks
 
If you use a shunt trip, presumably the MCCB would need a manual reset?

Whilst G59 relay / contactor would be automatic reset when genny off ?
 
it'd be useful to know what inverters you've used. I think both SMA and ABB would have control options that could be used to sort this out.
 
That's a soft input though isn't it Gavin? Resulting in an active but zero power state? Wouldn't an (electro)mechanical interlock be ideally required/preferred?

it'd still achieve the same thing though really. Ultimately the G59 settings should stop anything massively bad happening, but it'd not be a good situation to be in for long.

No idea about fronius though.
 

Reply to PV and Back up Generators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Afternoon! Hoping someone has experience working on the ABB gear below. It’s in a Mobile Office/ Welfare unit, supplied via either 230v hook up...
Replies
0
Views
200
I am a Napit registered electrician and want to get into Solar PV and battery storage. I have boot camp booked in April but am not hearing good...
Replies
1
Views
355
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Good day all, I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz. I'm managing a...
Replies
3
Views
1K
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
909

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock