kingbob

A friend had a pv array fitted which fed into a 16a mcb on the non rcd protected side of a split fuse board. The fuse board has now been brought up to date with the fitting of a second rcd so that all circuits are protected. Now unfortunately the rcd covering the side of the board that the array is on trips occasionally, sometimes several times in a short period of time. All the circuits test ok, insulation, e-n etc. Could the pv array be causing this problem
 
No, the person who put the pv onto a shared RCD has caused the problem.
unless certain rules apply, then pv should not be on an RCD but never on a shared RCD.
I hope this helps.
 
I would imagine if they looked at the cable from the inverter to the db it wouldn't require rcd protection, so wrong choice of distribution board.
 
Next time the RCD starts tripping out, turn off the breaker that is supplying the PV system. Try switching the RCD back on. If it stays on, leave it for a few minutes and then switch the PV breaker back on - if it trips then it is very likely that it is the PV system that is causing the problem - or at least the main part of the problem.

Regardless, your system needs attention anyway. PV systems should not be installed on a shared RCD - it needs to be on its own seperate breaker. The reason for this is that a PV system could still be producing power after the RCD has operated. Therefore, all of the circuits protected by that RCD could still be energised, at least long enough to mess up your disconnection times.

To be fair to the electrician that changed the board, it is not a generally well known problem - even amongst the PV installers themselves.
 

Reply to pv arrays and rcd protection in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Ok, installing a new CU with type 2 SP. The installation has an existing PV 6 panels protected by a 16a MCB at the fuse board. TBH I don't really...
Replies
0
Views
625
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock