Berns


Hi

I am gettingmyself prepared for G59 connection applications for PV systems. Guidance onwhat is needed with regards to technical date and drawings would be muchappreciated.

Withreference for the application form for 'e-on'

http://www.eon-uk.com/downloads/G59_APP_FORM_AW.pdf

Thisapplication applies to all generating source including spinning ones. Withregards to PV systems do anyone know what is required for parts 1A and B,especially the following:

Power station standbyimport requirements (see note A2)

Maximum active power import

____________________________MW

Maximum reactive power import (lagging)

___________________________MVAr

Maximum reactive power export (leading)

___________________________MVAr



Power station top-upimport requirements (see note A3)

Maximum active power import

____________________________MW

Maximum reactive power import (lagging)

___________________________MVAr

Maximum reactive power export (leading)

___________________________MVAr

Power station exportrequirements (see note A4): Total power station output at registered apacity (net of auxiliary loads)

Registered capacity (maximum active power export)

______________________MW

Maximum reactive power export (lagging)

______________________MVAr

Maximum reactive power import (leading)

______________________MVAr

Power station maximumfault current contribution (see note A5)

Peak asymmetrical short circuit current at 10ms (ip) for a 3short circuit fault at the connection point

___________________kA

RMS value of the initial symmetrical short circuit current (Ik”) for a 3short circuit fault at the connection point

___________________kA

RMS value of the symmetrical short circuit current at 100ms (Ik(100)) fora 3 short circuit fault at theconnection point

___________________kA



Kind Regards



BernardElliott

[email protected]


 
Last edited by a moderator:
Hi,
Did you get the info you required for the G59/2 if so could you pass it on as i am currently going through the same issue.

Rgds,
Az
 
Hi,

Same Same can anyone help on the G59 Application form or post a link/example completed application form so we know what the DNO requires.

Thanks

ACG
 
ACG, Which DNO? When we did our first one waaaayyy back, we just called and spoke to them, that way they got exactly what they wanted, not what we thought they wanted !

talk to them politely and they will nearly always be helpful.
 
Agree with Worchester.
I found that if I wasn't sure I would put what I thought they were after and then explain what my answer refers too. A few parts are N/A to smaller systems anyhow.
 

Reply to PV G59 application for connection with DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all, i'm a home owner just looking for some advice. Over Christmas the RCD on a split panel fuse box kept tripping. We narrowed this down to...
Replies
12
Views
6K
My view on life, in any field, is not to produce more but to consume less. Everybody told me this is a very eccentric weird mentality. Perhaps...
Replies
12
Views
2K
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Replies
0
Views
3K
the only part of the G59 form i have left to answer is the section part 1a: Peak asymmetrical short circuit at 10ms (ip) for a 3 short circuit...
Replies
9
Views
7K
tonyjones
T
Interesting discussion today with WPD, (My favourite DN0 :) ) with regards to extending an existing 3.68kW system. One pole, two overhead wires...
Replies
7
Views
2K
Ian-LS
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock