PV non MCS wow.

Discussion in 'Solar PV Forum' started by 1Justin, Oct 3, 2017.

Discuss PV non MCS wow. in the Solar PV Forum area at ElectrciansForums.co.uk.

Tags:
Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. 1Justin
    Offline

    1Justin Electrician's Arms

    Location:
    Surrey
    Business Name:
    Circitas Ltd
    I am undertaking EICR at a sprawling domestic over a house and several barns/guest suites, which is knee deep in C2 and C1 observations.

    I have here a ground-mounted PV install without any documentation, not an MCS install, and (I just spoke to DNO), they have no record of it on G59 or G83 and rightly say it needs to be disconnected until then.
    It's about 5 KWP, but had little time yet to check further. Two arrays of 10 panels ground mounted South with 2 inverters SRP Australia SR4200TL. Inverters mounted on the frames (which are wood).
    TT system, nearest earth stake is about 40M away at the board they feed into via 40A RCBO. (& sub-main to that board itself doesn't meet ADS).
    There is no export meter and main meter is disc-style (I suspect the old going-backwards type which may well be it's raison d'être.. but haven't checked).
    AC export/supply cables are unprotected blue "Arctic " flex, thrown into the soil and semi/entirely submerged on unknown route. There is a AC isolator on the wall of a barn about 15 M away and thereafter 10mm T&E thrown onto the floor of a barn back to the CU.
    No labelling of anything anywhere, no diagrams, no warnings.

    Give it to me..
     
  2. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    have fun.
     
  3. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    You looking for problems:D
     
  4. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Think he may have already found 1 or 2 Westy:D
     
  5. Scuba
    Offline

    Scuba EF Member

    Location:
    Glasgow
    I suppose it depends on what you were contracted to do? If it was to carry out an EICR then that's what you do to the best of your professional ability. After it fails with all the various problems it's then up to the owner to decide on the next course of action.
     
    • Agree Agree x 1
  6. 1Justin
    Offline

    1Justin Electrician's Arms

    Location:
    Surrey
    Business Name:
    Circitas Ltd
    Well the owner is using the whole area for paying guests as part of B&B. She needs "satisfactory" on an EICR yet has has a load of dodgy unregistered installation works done by builders, so wants all C1 and C2 cleared before I issue the cert.
    I have explained that all I can do is an EICR on what I can physically inspect and test, (not an EIC), and to put right all the C1 and C2 faults. If Building control is happy with an EICR for completion, (and not an EIC), then that's their decision. Owner thinks they will be.
     
  7. Scuba
    Offline

    Scuba EF Member

    Location:
    Glasgow
    It's your name on the bottom line of the report if someone gets fried......
     
  8. 1Justin
    Offline

    1Justin Electrician's Arms

    Location:
    Surrey
    Business Name:
    Circitas Ltd
    Agreed, hence EICR will be most explicit about limitations!
     
  9. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Sounds like years of rubbish to be identified and cleared out. Make sure they understand that and ask to approach it in stages, each invoiced. The report first and then the fixes in a couple of stages perhaps?
     
    • Like Like x 1
  10. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    Well the owner is getting a rather large bill from yourself or another contractor to bring all that lot up to standard and comply with the regs.. If building control knew the full extent I suspect they would be jumping up and down with glee as they do like a big case now and then to make an example of to fill the coffers of the state.
    Rather you than me as i would be very wary about putting my name to any certificate or report with loads of issues.
     